默认 how to calculate the maximum spacing between expansions join

how to calculate the maximum spacing between expansions join
i have concrete building has dimension (80 meter x 60 meter ) 5 floor i want to make expansion joint but the arch engineer refuse
i want to know if i can complete my design with out expansion joint or not, so i need any information or how to calculate the spacing between the expansion joint and if u know any web site can help me
this building has different temperature (22 inside and 55 out side)
swelm,
did you mean control joints?
expansion joint - you need it to separate the slab from other components such as wall, column, etc..
control joint - aci 318 recommended 3* slab thickness. for example, you have 4" thick slab, your control joints will be cut at every 12.
you may need an expansion joint. since you stated your problem in meters and degrees celsius i know you aren't in the u.s., but this may help....
i just have to chime in here, being an engineer trained in both metric and imperial, and having used both nearly every working day until my move to new zealand.
the imperial rule of thumb is as zestructural has stated, 3 times the slab thickness in inches gives you your maximum control joint spacing in feet.
the metric version is even more simple: divide your floor thickness by 0.028. done. units are consistent. i like to think about this as being akin to the minimum reinforcing in a slab... mind you, it is an order of magnitude off, but you get the idea for the mnemic.
quick summary:
3*slab" = jointspacing'
or
slab(mm)/0.028 = jointspacing(mm)
note that the metric version is conservative by around 2%. not all that great a concern, after all it is a rule of thumb (if a highly tested and often specified one).
good luck,
ys
b.eng (carleton)
working in new zealand, thinking of my snow covered home...
i think the poster is referring to building expansion joints - 80m building = 262 ft. wide.
for that width of building you probably don't need to
have an expansion joint to divide your building into
two separate structures. (based on aisc figure 1-1 in the
manual for concrete structures)
swelm
you have to look at the effects on the floor and the supports of the amount of shortening/movement you are going to get. most of this movement will be due to shrinkage and temperature change. for a pt building there will be some for the axial prestress as well. you need to calculate the moments and shears in the columns and the moments and axial forces induced in the floors due to the restraint of these movements. creep of the columns and the floor will reduce the effects but they are still very significant.
80m is larger than my preferred maximum limit of about 65m but the actual limit depends a lot on the structural layout, temperature change, concrete properties etc and a lower maximum may be necessary.
if the temperature during construction is 55c (i presume you are in the middle east to experience this temperature) and the temperature during operation is going to be 22c then you have a very large temperature change to deal with in addition to probably fairly high shrinkage as the building is obviously air conditioned.
thank you for everyone add to me new information,and try to help me
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
floor joist spacing huangyhg 产品功能分析 0 2009-09-09 12:44 PM
correct column tie spacing huangyhg 产品功能分析 0 2009-09-08 02:04 PM
calculating load on rebar to calculate embedmen huangyhg 产品功能分析 0 2009-09-07 10:00 PM
【转帖】dwg extension in world coordinates yang686526 DirectDWG 0 2009-05-05 08:01 AM


所有的时间均为北京时间。 现在的时间是 12:45 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多