默认 bearing on brick veneer a no-no

bearing on brick veneer a no-no?
in a situation with a cavity wall (6" stud + 2" air gap + 2" veneer with brick ties) i've heard that bearing anything on a brick veneer, say canopy trusses bearing on a ledger bolted to brick veneer, is a bad idea because the veneer degrades over time and really isn't reliable structural because of this reason...so instead all the canopy trusses should go through the brick veneer and bear on the backup studs/structure behind the veneer...has anyone heard differently?
find a job or post a job opening
hippo11,
there has been a post on this exact topic in the last couple of months, i suggest you do a search.
i believe that the responses were mixed.
csd
i did a "search posts" by keyword= brick veneer, bearing brick, brick, and didn't find anything!!
do you know what the subject of that thread was?
thanks!
hippo-
the search for this site is horrible. i have done searches on threads that i have started and knew very specific words to narrow it down and could only get threads from the mechanical forum (and even then only 1 thread, if any).
did you use the google option to search the site? i put in "brick veneer" and got this:
look in the aci 530 definition for veneer. that should answer your question. brick veneer is not load bearing by definition.
hippo -
your back up "wrinkled tin", wood or block is your only choice the apply external loads on.
the ledger bolted to the brick veneer is a bad detail looking for achance to fail. - eccentric load applied to a 2" veneer?
the direct approach of connecting to back up will also require the appropriate flashing and weeps to maintain the moisture barrier.
hippo11:
agree with others here. bearing on 2" veneer is just not a good idea.
a common solution i have seen and used for small canopies or additions in similiar situations is to run a beam parrellel to the face of the wall to collect the canopy trusses into two beam lines that poke through the brick venner to the backup wall space behind.
in the stud space, place steel columns to pick up the ends of the beams. the posts bear on the foundation walls (assuming the existing foundations will handle the extra load). in a 6" stud space, its fairly easy to get up to a decent size column with considerable axial capacity.
be sure there is some way to keep the whole thing from swaying so that you can consider the columns 'pinned-pinned'.
hippo11,
sorry i should have read your post more carefully.
2" is not a veneer is is really just a cladding - 2" masonry should never be taken as load bearing.
csd
here's a link to a similar thread:
hippo11,
from the aci: veneer, masonry, a masonry wythe that provides the exterior finish of a wall system and transfers out-of-plane load directly to a backing, but is not considered to add load resisting capacity to the wall system.
so the short answer is no. technically, once you add load to the veneer, it is no longer a veneer system and must be designed as a load bearing wall, subject to all requirements. you will likely have to modify the wall in some way, such as adding steel or light-gauge metal framing to pick up the load of the trusses. or, you could do something with solid masonry (piers and a bond beam.) it depends on the structure and overall design.
for additional information, go the the bia website for free downloads of their technical bulletins.

the masonry institute of american also has information, but requires a membership. your local jurisdiction will probably reference the aci. mine uses 530-05, building code requirements for masonry structures. aci also requires membership.
is your brick veneer really only 2-inches? the minimum size required is generally 2-5/8鈥? two-inch material is normally adhered, not used in cavity wall construction.
"if you are going to walk on thin ice, you might as well dance!"
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
bearing capacity of thru-bolts on brick huangyhg 产品功能分析 0 2009-09-07 03:14 PM
anchor brick failure - could cause be water huangyhg 产品功能分析 0 2009-09-07 11:55 AM
allowable bearing capacity huangyhg 产品功能分析 0 2009-09-07 10:51 AM
8 masonry back-up to 4 brick wall huangyhg 产品功能分析 0 2009-09-07 08:58 AM
27 feet high brick 9clay0 masonry wall huangyhg 产品功能分析 0 2009-09-07 08:33 AM


所有的时间均为北京时间。 现在的时间是 10:32 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多