几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量  


返回   几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量 » 三维空间:产品设计或CAX软件使用 » CAD设计 » 产品功能分析
用户名
密码
注册 帮助 会员 日历 银行 搜索 今日新帖 标记论坛为已读


回复
 
主题工具 搜索本主题 显示模式
旧 2009-09-07, 08:58 AM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 8 masonry back-up to 4 brick wall

8" masonry back-up to 4" brick wall
i have a couple of questions. when calculating the value "d" for rebar location in a grouted masonry cell, is it common to use 1/2 the block depth? i've normally used .45 x block depth. is that too conservative?
i've done some split-face block design before, but never played around with brick veneer. the contractor deviated from my 10" cmu design and used an 8" block with 4" brick. he is contending that the brick adds to the strength of the wall (there is an air space between.) to me, it seems that the ties only transfer the load to the block, which does all of the work. is there a way to increase the capacity of the 8" block wall with the 4" brick?
thanks
the brick is strictly a non-structural veneer, since there is no means to transfer the load between the different wythes.
you just got a very fine 8" bearing wall with great weather resistance (no more insulation though) if the reinforcement spacing is the same. the wall built is not as strong (for flexure) as the 10" wall you designed. there is no practical way to increase the flexural strength of the wall unless you want to be exotic and apply sheets of kevlar to one side of the wall. you probably have more compressive strength that you need since the astm c90 strength requirement are so low that manufacturing methods/material handling usually produce block well beyond astm minimums. i know of block producers that cannot afford to make minimum stregth and typically are 40-60% over astm requirements. obviously, that has all but eliminated the concept/availability of non-loadbearing cmus except for specialized uses.
many engineers take the easy conservative route and use 1/2 of the block thickness for d, but you can specify a greater one by requiring the reinforcement placed close to one face or the other. for an 8" block wall you can get a d of just under 6" if the location is specified and controlled.
you must make sure grout (8" to 11" slump) is used in the filled cores and not mortar or concrete.
dick
ivany block have slots for positive location of reinforcement adjacent to both faces prior to grouting. this is the only type of block that i would use a d greater than 0.5 depth. the brick adds nothing flexural strength wise unless bonded to the block.
thanks to each of you for your feedback. that is very helpful. i have a hard enough time in getting masons to even look at the drawing, much less follow a specification to place the rebar a certain place in the hole so i think i'll stick with 1/2d or .45d to be safe.
postframese -
i understand your quandry. that is why many engineers take the route of putting the bar near the middle and use extra rebar and grout.
many areas do not have good mason contractors that bid jobs in a price-oriented market situation or project. the good masonry contractors make money by charging a reasonable (not cheap) price and getting the job done on schedule and according to specs. usually, they have a long term relationship with the gc, although in some markets gcs do their own masonry because of the importance of scheduling. some masonry subcontractors are just blocklayers.
the key is good job site inspection or enforcement of the design specified, after you have a reliable mason contractor. often, a good strong position at a pre-construction meeting will go a long way to sort out what is really critical. i saw a project of 20 - 15 to 22 story, 6" loadbearing partially reinforced block (4 different strengths) buildings built with very few clean-outs or job site prisms because of good, detailed quality control measures taken in advance. - it was cheaper to design it correctly nad build it right than to assume a lower standard and add extra material and labor to the cost.
there are many methods and/or products that insure rebar placement if a specific location is requird. civilperson's suggestion about the "ivany" block is just one. george ivany was a structural engineer that was involved in many multi-story (3 to 7 story) loadbearing masonry buildings. there are also similar uints or rebar spacers that can be used to insure the location and eliminate the detailed inspection of each grout core. the use of specilized block is more consistant and eliminates the ordering, scheduling and placement problems common to using hardware.
good luck!!
dick

it would seem to me that if there were adequate joint reinforcing tying the veneer to the block backup and the brick assembly were of adequate strength, then the load could be estimated to be distributed to the block and brick based upon their individual stiffnesses.
comment to jkw05 post:
unless the brick veneer was on both sides of the block, then the flexural strength would differ for each type of moment. the joint reinforcement would function similar to the web steel of joists and the compressive block would exist in the brick, (exterior fiber), making the block a interior element only used to transfer shear. it would be an interesting problem to model brick as a composite structural element in flexural/axial loading case.
jkw05 -
the key word is "if". the tie between the two wythes must be able to handle the vertical shear required for the 2 wythes (block & brick) to act as a composite section - very difficult. it appears flexural equivalency is the concern.
dick
i'm not thinking of it as a composite wall. i'm thinking of it as an 8" wall carrying a percentage of the load, and a 4" wall carrying a percentage of the load. the percentages would be based on the relative stiffness of each individual wall. the joint reinforcing links the two walls together, forcing the two walls into consistent deflections. stresses for each indvidual wall would need to be within allowable values.
jkw05
i believe you are correct, that proper ties allow load distribution. i have a publication by the portland cement association that states that "each wythe in a cavity wall hepls to resist the wind acting as a separate wall." it has graphs representing this reprinted form the "masonry structural design of buildings, tms-809-3, department of the army, or afm 88-3, chapter 3, department of the air force. these should be available on line.
put the minimum required eccentricity on the axial loaded wall or apply horizontal loads from wind or seismic, and the flexural strength becomes relevant. thus the model you describe is still required to be within the p-m diagram.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
42 tall cmu firewall huangyhg 产品功能分析 0 2009-09-07 08:47 AM
27 feet high brick 9clay0 masonry wall huangyhg 产品功能分析 0 2009-09-07 08:33 AM
20 high basement wall and diaphragm huangyhg 产品功能分析 0 2009-09-07 08:23 AM
9un0cracked masonry section huangyhg 产品功能分析 0 2009-09-06 10:21 PM
【转帖】adtdirect wall geometry yang686526 DirectDWG 0 2009-05-04 03:52 PM


所有的时间均为北京时间。 现在的时间是 09:48 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多