几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量  


返回   几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量 » 三维空间:产品设计或CAX软件使用 » CAD设计 » 产品功能分析
用户名
密码
注册 帮助 会员 日历 银行 搜索 今日新帖 标记论坛为已读


回复
 
主题工具 搜索本主题 显示模式
旧 2009-09-16, 10:53 PM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 wood framed shear walls in single family residence

wood framed shear walls in single family residence
i am trying to get some other practicle opinions on how working engineers actually handle the lateral design of wood framed single family dwellings in seismic zone 2 or 3 areas. i have read several articles and papers on the controversy of designing walls for flexible diaphragm (shear load distributed based on wall length) and rigid design (shear load distributed based on stiffness). there does not seem to be a clear consensus and the whole house test data and historical data don't clear up the matter. i know there are programs like woodworks and latpro that will calculate the distribution of shear walls but they are only as good as the assumptions you give them. is the load distribution diaphragm flexible or rigid or somewhere inbetween? how do interior gypbd shear walls affect the distribution? if your building is over 34 feet between exterior walls you have to use interior gypboard shear walls and even if you don't count them those interior walls will affect the shear distribution. how much does the quality and care of the builder affect the strength. building departments sometimes require a table from the engineer showing the distribution of shear forces to every shear wall throughout the building. there are a lot of assumptions go into how the shear is distributed. in this forum i see a lot of recommendations for using rigid diaphragm design and stiffness and then comments that they prefer to do this by hand rather than with a program like latpro or woodworks. the true lateral stiffness of each panel depends a lot on the location of each holddown. do engineers detail out every shear wall with all the hold downs and sheathing orientation. this is the reccomendation of some groups such as the curee project at
i can only give you a comment from the distance, since we (in spain) don't practice at all such kind of construction.
according to the general good practices of the science of construction as i understand them now, any lateral strength coming from purportedly non-structural panels would be outrightly dismissed for all design purposes. the lateral resisting system sets a warranted and tolerable level of lateral deformation for everything else. the contrary would be in my view an alternative adopted with some special target in mind, usually solving some technical or economical problem.
then, if you ensure firm tie-down of the lateral resisting panels, one should assign the solicitations as their stiffness at their place demands. this is not so difficult once one owns 3d design programs. other thing is that by code or other aceptable engineering source one may be able to use simplified ways to assign forces for the individual design of the shearwalls, but this is to be in my opinion to be thought worse than what above.
respect details, here it is expected that the drawings contain anything of structural meaning. however it is obvious that (out of this field) there remains work for steel fabricators, precast providers and even reinforcement detail if someone is asking more detail than usually provided. this also uses to go a lot with the kind of work, premium jobs (of higher fees) are expected to hold more detail, sometimes quite exhaustive. in the end i think that if the drawings are meant to be used in a limited areaa where there is definite custom of having or not such and such detail, that might turn acceptable practice as long as the code does not demand otherwise. yet, out of professional responsability, one must always express anything it thinks required for the satisfactory construction of his design.
right, this is a simple yet complex question, which can have many answers.
in seismic zones 2 & 3 wind usually governs lateral force requirements in wood frame construction (unless the building is unusually heavy).
we usually try to keep the aspect ratio of the building (width to depth) to 1.5 to 1 by cutting the building into a series of boxes. a building 26' x 78' would have an interior shear wall around 39', or as close as possible. never mind all those gyp board shear walls (they do not have much value).
walls that do not have any openings are a bonus. walls that have openings have to be calculated according to the piers and can be cumulative for the length of the wall, adequate holdown against uplift must be provided at piers.
in california in seismic zone 4 we usually list every shear wall, drag strut, and reference to details on a seperate sheets devoted just for that purpose (shear plan). on a single story residence the roof plan contains diaphragm elements, such as drag trusses and reference to details. on a two story residence the floor diaphragm elements are listed on the second floor framing plan with reference to details.every connection must be detailed (sometimes 100's). all shear walls, diaphragms, hold down requirements, fastener schedules, etc. are required to be calculated in the engineering report.
i do not like to use or specify gypsum board shearwalls, they just don't do what they are intended for (over rated). thermo-ply structural grade red .113 is a good choice under gyp board.
anyway i could go on forever.
the link above is an experimental project, and the results (they hope) to be used in future building codes, or at least that is what i got out of it.
a plywood diaphragm acts as a horizontal deep beam to collect and transfer lateral forces to the shear walls. structural wood panels form the beam web to resist shear force, purlins act as web stiffeners, and the boundary members normal to the load form the flanges to resist flexural effects. shear stresses are assumed uniformly distributed across the depth of the diaphragm. the boundary
try "timber solutions manual " author;david w. duquette p.e. publisher da vinci publishing, new york, new york. 1997 isbn: 0-9656181-0-2 cost 49.95 dollars us
thanks guys. i still have a hard time believing that all the practicing engineers out there when they have a single family residence that is not prescriptive do a deflection analysis of the roof and floor diaphrams to determine if they need to consider the structure as rigid or flexible for shear wall load distribution and then detail out every floor and roof diaphragm and shear wall. maybe i'm just lazy or i don't charge near enough.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
shear key at base of walls huangyhg 产品功能分析 0 2009-09-15 09:43 PM
rigid distribution of wood shear walls huangyhg 产品功能分析 0 2009-09-15 06:57 PM
multistory wood shear walls, overturning and uplif huangyhg 产品功能分析 0 2009-09-10 03:29 PM
can i count on shear-friction capacity of the reinforcemen huangyhg 产品功能分析 0 2009-09-07 10:22 PM
block shear vs. shear rupture at connections huangyhg 产品功能分析 0 2009-09-07 03:57 PM


所有的时间均为北京时间。 现在的时间是 07:45 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多