torsion capacity in existing rc beam
i have run into a situation on a cantilevered slab that monolithically ties into a rc beam. the proposed loading will result in an applied torsion that exceeds the torsion capacity of the rc beam. the rc beam does not have the tied (torsion resisting) stirrups, so i analyzed the capacity of the concrete section per aci 11.6.1, limiting the capacity to the cracking torque tcr. is there any additional torsion capacity that is provided by the shear stirrups (u-shaped)?? right now, it appears that my only solution is to reduce the torsion in the cantilevered slab by adding a column or some other sort of bracing near the edge of the slab. thanks in advance for any advice. p.s. this is a great site - i just stumbled on to it this morning.
samenella,
the u-shaped stirrups provide shear/torsion reinforcement for the two sides and the bottom of the rc beam. the reinforcing bars in the cantilevered slab that extend through the top of the beam and are anchored (by hook or by development length) could take torsional shear stresses on the top of the beam.
i believe you could consider the excess area of those bars, not needed to carry the moment in the slab, as contributing to the torsional reinforcement of the beam.
aef
i do not believe that the u-shaped stirrups are effective in resisting torsion. but does the slab continue past the beam? if so, the back span of the slab and the beam itself will share the negative moment based on their relative stiffnesses. since the bending stiffness of the back span is probably a lot larger than the torsional stiffness of the beam, the beam will not see much torsion.
daveatkins
dave,
the slab does in fact extend beyond the rc beam. to give you a little background - because of the relatively complex loading (circular loading pattern with 8 bearing pads) and complex slab-column-circular wall system - i have modeled using staad. to my knowledge (this is my first floor system i have modeled with staad) the stiffness of the beam and slab have been accounted for in determining the applied torsion to the beam. intuitively i would agree with you that the "back" slab would provide significant stiffness, but i'm relatively confident that this has been modeled in staad and the applied torsion that i'm seeing in the beam is reasonable. however, i'm also inclined to believe that the excess moment steel in the slab would provide at least some additional torsional capacity. any ideas on how to better quantify this mess??? thanks for your help.
i worked on a parking structure once where my supervisor told me that once a r/c beam fails in torsion, then the moment is redistributed to the slab. we justified an existing beam on that project in this manner, but i must admit i was not 100% comfortable.
aci 11.6 covers torsion design quite extensively. section 11.6.1 gives the maximum "ignorable" torsion. section 11.6.2.2(a) gives the maximum torsion that must be designed for, since in this case any additional torsion can be redistributed to the slab. section 11.6.4.1 discusses using closed stirrups for torsion.
forgive me if you have already reviewed all those sections. back to the original question--if you can get comfortable with assuming the top steel in the slab plus the u-shaped stirrups together act like closed stirrups, then i think you can justify what you are doing. conceptually, this idea has merit. but i have never justified resisting torsion in this way.
i would check, by hand, the relative stiffnesses of the beam and the slab, to make sure staad is not overestimating the torsion.
daveatkins
using staad, probably you are modelling the slab by shell elements that are connected to the beam at some nodes in the geometric center of the beam. i believe that the statical torsional moment you get by staad is correct, but the deflection is probably overestimated since if beam and shell elements are added this way staad simply adds their corresponding stiffness and does not calculate the combined stiffness that results due to the effective width of slab that is working together with the beam. i think that you should assume an angle cross sectional form comprised of beam and effective width of slab in your capacity calculations. then estimate deflections with the cracked properties of this section using staad statical torsional moment.....
i also believe that you can assume some 'closed stirrup' action due to the negative reinforcement of the slab, but probably not to full yield...
thanks to you all for your help in this matter. this is an excellent site, and i feel fortunate to have stumbled upon it. cheers
sam, an aspect that you could check is whether the formulation of the shell elements used to model the slab includes or neglects transverse shear deformations, since, depending on the span-to-thickness ratio, they would be affecting the torsion output in varying degree.
also: are you taking into account in the concrete section resisting shear the solid slab forming the flanges of the t beam?
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
new to existing concrete beam connection huangyhg 产品功能分析 0 2009-09-10 04:22 PM
existing beam - added shear capacity huangyhg 产品功能分析 0 2009-09-09 08:51 AM
escalator span for existing beam to beam spacing huangyhg 产品功能分析 0 2009-09-08 10:52 PM
cantilevered steel i-beam capacity huangyhg 产品功能分析 0 2009-09-07 10:45 PM
12 x 6.5x 38 thick x 41 residential basement i-beam con huangyhg 产品功能分析 0 2009-09-06 10:30 PM


所有的时间均为北京时间。 现在的时间是 01:09 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多