too much reinforcing in concrete wall?
i am working on a wwtp where the precaster would like to keep a wall thickness to 14". i can make this thickness work for the loads, however, the reinforcing is becoming quite heavy on the inside face mat. i would need to use #9 bar @ 4" o.c. although this still falls below the maximum steel ratio and the spcaing of the bars is wide enough to allow the largest aggregate to easily pass through i am having concerns about this configuration. what are your thoughts? is there a good reason that i should insist on going with a thicker wall?
thanks
as long as you meet the reinforcing requirements per aci 318, what's wrong? can you use a larger bar size?
before attending an aci seminar not too long ago i would not have thought much of it. during the seminar the speaker worked through a sample problem and the reinforcing came out to #8 bars @ 5" o.c. which he dismissed as unrealistic and went to a thicker wall. this stuck in my head because i could re
in my mind #9 @ 4 inches are too close. even if you meet the maximum reinforcing ratio in the old code of .75*rho balanced, you're probably not going to meet the strain restricted requirements of the aci 318-02. not to mention, there's not going to be very much clearance between wall bars, especially when you put in the steel in the other direction. we had a engineer in our office attend an aci seminar and they said that you should try not to exceed 1.75 percent.
how tall is your wall? what are the load conditions that require a 14" thick wall? are you resisting both gravity and wind/seismic loads? if you think about the wall being a simply supported beam 12" wide and 14" deep, would 3 #9 bottom bars be too close together? if you think of the wall as a 12" wide x 14" long column, would 3 #9 bars on one face be too much? perhaps that's oversimplified, but as long as you satisfy all of the reinforcing criteria of aci 318 for the design, which includes the strain criteria, the #9 at 4" o.c. should be ok.
the wall is 18' tall. the loading condition that is being designed for is soil pressure plus a large surcharge.
i might not be as concerned about the #9 @ 4" in the wall as i would be in making sure the connection from the wall to the foundation is healthy enough to take what sounds like a very large moment. i mean, the #9 @ 4" sounds excessive, but if it works, it works. can you increase concrete strength to get a little larger spacing?
although aci 350 does not appear to have a wall deflection criteria, i would suggest that you calculate and be comfortable with your wall deflections. pca publication "rectangular concrete tanks" has wall deflection coefficients.
they will have a lot of difficulty not getting voids - especially if the wall is tall.
#11@6" may be better for setting concrete - if it works numberwise.
just re
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
reinforcing on concrete blocks walls huangyhg 产品功能分析 0 2009-09-15 05:42 PM
in enercalc masonry wall design, what is parapet heigh huangyhg 产品功能分析 0 2009-09-09 07:17 PM
foundation wall 40 feet below grade huangyhg 产品功能分析 0 2009-09-09 01:38 PM
concrete seawalli-wall huangyhg 产品功能分析 0 2009-09-08 12:35 PM
chapter 4 preliminary design properties of concrete huangyhg 产品功能分析 0 2009-09-07 11:23 PM


所有的时间均为北京时间。 现在的时间是 04:25 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多