tension on top anchor at welded shear tab connection
we have an embed plate in a concrete wall. a shear plate is welded perpendicular to the embed plate and a beam connects to the shear plate. if the beam were bolted to the shear plate, the tension in the top anchors would be calculated by multiplying the gravity rxn by approx 3" (dist from face of plate to bolt line), then dividing by depth to bottom bolt. however, if we weld the shear plate to the beam rather than bolt the beam, have we increased or descreased the tension in the top anchors?
two schools of thought:
1. the beam and plate welded have "become one" (the weld resolves the moment)and now the gravity rxn is at the end of the shear plate, basically at the face of the embed plate. this creates very little tension on the top anchor.
2. by welding you've moved away from the pinned connection to a moment connection which introduces a higher moment into the top anchors.
these are opposite schools of thought. either look correct? neither? why? thanks.


i think it would depend on the stiffness of the shear plate.
if you weld a relatively small shear plate that does not extend the full depth of the web
the first one is more accurate, in my opinion. it's all about stiffness. the welds are inherently much stiffer than bolts. welding to the embed plate and bolting to the beam makes the shear tab act like a cantilever and the bolts as a pin.
when you weld the shear tab to the beam, the tab (as long as the plate/weld can take the moment) act as one beam (as you noted) and deliver mostly shear to the embed plate. the reason i don't believe it will increase the tension in the top anchor is that the elastic negative moment at the support can't be supported..... the plate capacity is small compared to the beam so it will act simple. that being said, there is some stiffness there, so some moment (and tension in the top anchor) will be there, but certainly less than with bolts.
only a full analysis could tell you what the effect on the moment is.

my strategy would be to limit the failure mechanism.

you do not want failure at the weld or in the embedded anchors.
therefore, check your plastic bending in your shear plate and make sure your weld and embedded anchors can take that maximum moment.
if this works then you have a plastic hinge at the shear plate and the moment on the weld and embedded anchors will not exceed your plastic bending.
i think some people are missing the actual question. the question was only about relative tension in the top anchors when the shear tab is welded to the beam as opposed to bolted to the beam.
i took this to mean that for a given shear tab with a given embed plate and a given beam with given loading.... will the top anchors in the embed plate have more or less tension in them if you weld the shear tab to the beam as opposed to bolting it.
i don't see how the answer can be anything other than less tension.
streit-
all things being equal, you are right. i agree that for the same shear plate, a welded condition would result in a smaller tensile force in the bolt at the top.
if you design the bolts or welds to the beam for the eccentricity, then you do not also have to design the plate for the eccentricity from the face of the plate to the bolt line or weld line. if the bolts or welds to the beam are not designed for the eccentricity, then your embed plate must be designed for it.
i've always learned that welds are inherently much more stiff than bolts (unless you provide a slip critical connection) and as such, if you provide bolts to the beam, the shear tab will act as a cantilever regardless of whether the bolts can take the moment or not because they will allow more rotation than the welds before resisting the moment.
is this an inaccurate statement?
the end rotation of the connecting beam must occur in one of the following locations:
1. at the weld - unzipping and failure
2. at the shear plate - plastic hinging
3. at the embedded plate to concrete interface - yielding of your headed anchors or potential concrete rupture (not recommended)
4. at the concrete itself - concrete is usually fairly stiff so this is probably not the case
i would not recommend allowing the rotation at the steel to concrete interface.
agree with ucfse.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
shear tab welded to supporting member and supported member huangyhg 产品功能分析 0 2009-09-15 09:56 PM
shear tab connection huangyhg 产品功能分析 0 2009-09-15 09:55 PM
hss beam to hss column shear connection huangyhg 产品功能分析 0 2009-09-09 06:01 PM
can i count on shear-friction capacity of the reinforcemen huangyhg 产品功能分析 0 2009-09-07 10:22 PM
block shear vs. shear rupture at connections huangyhg 产品功能分析 0 2009-09-07 03:57 PM


所有的时间均为北京时间。 现在的时间是 03:06 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多