snow loads around mech units
something that really bothers me about the canadian code is when it comes to snow drifts around rooftop mechanical units. the code states it isn't necessary to consider extra snow load if the width of the obstruction is less than (3.0*ground snow load)/unit wt. of snow.
here in winnipeg, this translates into a maximum obstruction width of about 5'-6". once you get over that width, then the snow load suddenly jumps up to 75 psf max (from 33 psf basic snow load) and the length of drift goes out a minimum of approx. 10'-0" or twice the unit height.
when it comes to replacing rooftop mechanical units on renovation jobs we often end up getting into beefing up the existing structure to handle these drift loads. then i get the "look" from the architect and mechanical guys like i'm from another planet.
some questions.....
1. what if one side of the unit is less than 5'-6", but the other side is say 6'-0". would you only conside drifting on two sides?
2. what about if you had a unit that was 5'-6" by 5'-6". if the wind blows at the corner of the unit then the projected width is now greater than the minimum. would you only get drifts at the four corners or can you ignore drifting all together?
3. when checking roof design, i usually account for the dead load of the unit plus the basic snow load on top of the unit. is that right, or would you reduce the snow on top of the unit due to wind scouring?
4. what would the actual drift shape around a mechanical unit look like, with the prevailing winter winds from the northwest? i always assume the full drift load all around the unit but is there any way to reduce it?
i share your frustration in dealing with the snow pileup issue around mechanical units. there is no logical answer to give an owner except to show him the code requirements.
as for your queries, this is how i handle those issues.
1. we use the pileup extent on the side required and extend pileup on the short side a distance equal to the height of the unit.
2. we look at the actual lengths. the code requirements are already ridiculous.
3. we usually include minimum live load of 1 kpa on the unit.
4. we also use drift on four sides. there does not seem to be a reference to allow for prevailing winds in the code.
one interesting idea i have heard of was to raise the units above the roof 2 to 3 feet to allow for the wind to travel without depositing the drift. i have not found any reference to this so i have been hesitant to use it.
hope this helps.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
snow loads - drifting sliding huangyhg 产品功能分析 0 2009-09-16 12:06 AM
snow loads arch roofs huangyhg 产品功能分析 0 2009-09-16 12:06 AM
snow drift loads in the sierras huangyhg 产品功能分析 0 2009-09-15 11:57 PM
new york 2007 code snow loads - reduced huangyhg 产品功能分析 0 2009-09-10 04:23 PM
deck with snow and live loads 9at the same time0 huangyhg 产品功能分析 0 2009-09-08 04:37 PM


所有的时间均为北京时间。 现在的时间是 08:52 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多