shallow footing design
typical spread footing with pedestal to grade. the building supplier provided the vertical and lateral loads. for design purposes can you reduce the lateral load applied at the pedestal height due to the constraint of structural fill and a slab on grade, or do you multiply the full lateral load by the height of pedestal and footing to determine the moment applied to the footer.
i would not recommend reducing the lateral load due to the presence of structural fill nor a slab-on-grade.
are you describing a foundation for a metal building system? if so, it is common to use a reinforcing bar wrapped around the anchor bolts to transfer lateral load into the slab-on-grade. i don't see any reason why you shouldn't use the slab to resist lateral loads, as long as you are providing a load path to get the force into the slab, and as long as the slab can resist the load in sliding.
i would consider both the use and importance (per building code) of the structure. for an industrial structure where changes, over time, are likely or for essential services (say a hospital), jike's recommendations sound good.
for a competitively priced building, perhaps a small retail store, mikee55's approach should be both satisfactory and cost effective.
does anyone use full depth footings sized for the uplift, over-turning, and vertical downward force? my thought is that more concrete is used but the time to form the pier, the extra pour, and the extra cure time is deleted.
i size footings for uplift, overturning and the downward force. also, i use the hairpins in the slab whenever possible. if the horizontal forces are larger than what can be transferred using hairpins, i've used tie beams between the rigid frame columns.
do you have a reference for the use of hairpin in slabs. won't that then present a problem with curling and shrinkage. slab size is 90 x 75
use of hairpin in slab is used to develop the dead weight of the slab and to restrain the top of the pier from the lateral forces by developing friction between slab and subgrade, however our office has started putting the vapor barrier under the slab and not the subbase, this reduces coeff. of friction, not sure to what, i thought i saw that on another thread. anyone know?
i have a few basic questions about the use of hairpins. do you eliminate slab joints so as to carry the tensile forces thru the slab? how do you deal with slab shrinkage. doesn't a hairpin defeat the isolation joint between the slab and the foundation wall? how do you prevent the owner from cutting the slab in the vicinity of the column?
i tend to relocate the slab joints away form the columns. the hairpin does tie the slab to the pier/wall but i think it is still pretty local. you can not prevent the owner once it is in his hands, same could be said of tie rods. its the plumbers you have to watch out for.
i've used hairpins on many metal buildings without any problems. however, you must keep in mind the flow of construction. many times the foundations are installed, backfilled and the building erected -- then the floor slab is poured under the cover of the roof. but, during that period between completion of the building shell and the curing of the floor slab the hairpins aren't effective. so, pray for no high winds and not heavy snows!
also, as others have noted above, if the floor is cut at sometime in the future, the hairpins could also be cut too.
as to the use of a vapor barrier, yes it reduces the coeff. of friction between the slab and the subgrade, however you could compensate with longer hairpins tied to the slab reinforcing. check the calcs once to verify the difference.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
reinforced concrete building design step-by-step huangyhg 产品功能分析 0 2009-09-15 05:12 PM
in a design and built contract,i ha huangyhg 产品功能分析 0 2009-09-09 07:16 PM
footing is too small for residential addition1 huangyhg 产品功能分析 0 2009-09-09 01:04 PM
design of continuous or strip footing huangyhg 产品功能分析 0 2009-09-08 05:37 PM
design build huangyhg 产品功能分析 0 2009-09-08 05:13 PM


所有的时间均为北京时间。 现在的时间是 08:47 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多