默认 reinforced masonry deflection

reinforced masonry deflection
i am aware of the limit of l/600 on unreinforced masonry deflection, but i am not aware of a limit on deflection of reinforced masonry. does anyone know of a code or an orginization that would give this reinforced masonry deflection limitations? thank you...

canadian code requirements span/480 (thank goodness for cut and paste):
12.4 beams-deflection
12.4.1
deflections of beams shall be checked when the clear span exceeds 15d.
12.4.2
immediate deflections shall be computed using the modulus of elasticity, e,, for masonry as specified in clause 8.3.1 and the effective moment of inertia of clause 8.3.2.
12.4.3
the total immediate plus long-term deflection may be determined in accordance with clause 8.3.
12.4.4
total immediate plus long-term deflection of beams shall not exceed span/480.
8.3.1 modulus of elasticity
8.3.1 .l
the modulus of elasticity of steel reinforcement, es may be taken as 200 000 mpa.
8.3.1.2
the modulus of elasticity, es of masonry made of concrete or clay units shall be determined in accordance with clause 8.3.1.4 or may be taken as es = 850f'm mpa but not greater than 20 000 mpa.
8.3.1.3
the modulus of elasticity, em of masonry made of stone or other types of units shall be determined in accordance with clause 8.3.1.4.
8.3.1.4
the modulus of elasticity of masonry determined experimentally shall be based on the secant modulus of at least five prisms tested in accordance with csa standard can/csa-a369.1. the modulus shall be measured over a stress range extending from 0.05 to 0.33 of the measured mean prism compressive strength. the modulus shall be based on the average value.
8.3.2 effective moment of inertia for deflection calculations at specified loads
8.3.2.1
the effective moment of inertia, ieff to be used in deflection calculations for reinforced and unreinforced walls and columns and for reinforced beams shall be calculated in accordance with clauses 8.3.2.2 to 8.3.2.4.
note: for the determination of the effective moment of inertia for very slender walls, see clause 11.2.4.3.3.
8.3.2.2
unless stiffness values are obtained by a more comprehensive analysis, immediate deflection shall be calculated using the modulus of elasticity for masonry, em specified in clause 8.3.1 and the effective moment of inertia, ieff determined as follows, except that ieff shall not be greater than io:
ieff = (mcr^3/ma)*io + (1 - (mcr^3/ma)*icr)
where
mcr = (phi*ft + fcs)*io / yt
ft = the appropriate flexural tensile strength value from table 6
fcs = unfactored axial load, p, divided by a,
ma = maximum moment due to specified loads.
icr may be calculated with the effects of axial loads included.
8.3.2.3
for continuous spans, ieff may be taken as the average of the values from clause 8.3.2.2 for the critical positive and negative moment sections. for prismatic members, ieff may be taken as the value obtained from clause 8.3.2.2 at midspan for simple spans and at the support for cantilevers.
8.3.2.4
unless values are obtained by a more comprehensive analysis, the total immediate-plus-longterm deflection for flexural
there was an erratum to the code, and
ieff = (mcr^3/ma)*io + (1 - (mcr^3/ma)*icr)
should read:
ieff = [(mcr/ma)^3]*io + [1 - (mcr/ma)^3]*icr
thank you...that is very helpful.
i guess the cut and paste is not foolproof, either... i think that's got 'em all...
12.4.2
immediate deflections shall be computed using the modulus of elasticity, em for masonry as specified in clause 8.3.1 and the effective moment of inertia of clause 8.3.2.
8.3.1.2
the modulus of elasticity, em of masonry made of concrete or clay units shall be determined in accordance with clause 8.3.1.4 or may be taken as em = 850f'm mpa but not greater than 20 000 mpa.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
masonry cemen huangyhg 产品功能分析 0 2009-09-10 12:28 PM
in enercalc masonry wall design, what is parapet heigh huangyhg 产品功能分析 0 2009-09-09 07:17 PM
deflection of beam supporting a concrete slab huangyhg 产品功能分析 0 2009-09-08 04:57 PM
deflection limits for masonry support members huangyhg 产品功能分析 0 2009-09-08 04:55 PM
brick cladding deflection limits huangyhg 产品功能分析 0 2009-09-07 04:48 PM


所有的时间均为北京时间。 现在的时间是 02:41 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多