re: combined tension and shear in bolts
i'm looking at the interaction equation aisc (j3-3b), page 16.1-109, aisc steel manual, 13th ed. solving for f'nt ≤ fnt. for a325 bolts, fnt = 90 ksi tension and fnv = 48 ksi shear from aisc table j3.2 and ω = 2.00 in asd. this means that all the terms in equation j3-3b are constant except the shear stress fv.
if i have a connection that has both moment and shear and m = 118.5 ft-kips and v = 9.8 kips on a w14x38 (14.125" deep) then:
c = t = m/d = (118.5 x 12)/14.125 = 100.67 kips tension
this implies:
no. of bolts = t/fnt = 100.67 kips/19.9 kips/bolt = 5.06 bolts
for shear:
no. of bolts = v/fnv = 9.8 kips / 10.6 kips/bolt = .92 bolts
choose five (5) bolts and check the interaction equation:
f'nt = 1.3*fnt – (ω*fnt/fnv)*fv ≤ fnt = 1.3*90 – (2*90/48)*fv ≤ 90
for five (5) ?" bolts fv = v/ab = 9.8/(5*.442) = 4.43 ksi
plugging this into the interaction equation:
1.3*90 – (2*90/48)*(4.43) ≤ 90 gives 100.4 ≠ 90
for seven (7) bolts 105.1 ≠ 90
for nine (9) bolts 107.8 ≠ 90
and for two (2) bolts 75.4 ≠ 90
how can fewer bolts be better???
now there is a user note saying that if the tension or shear stress is less than 20% of the allowable we can ignore the combined effect. this only confuses me more, since i would think the formula should work in either case. can someone point out what i'm missing?


fewer bolts is not better. the f'nt you are calculating is the available tension stress based on the actual shear stress that you have in the bolts. that being said, you can't have f'nt > fnt.
your calcs bear that out. for 7 bolts, f'nt = 105.1ksi, for 9 bolts f'nt = 107.8ksi.
i would also point out that your fv would be changing with the increased number of bolts (which you don't account for).
i think you are confusing what you should be comparing.
once you solve for f'nt, you should be comparing this to the actual tension in the bolt (service or factored), not the maximum allowable f'nt.
daveatkins
all the numbers were on a per bolt basis and yes, i realize that as the number of bolts increases, the stress per bolt is going down. i guess i was expecting an interaction expression that resulted in a specific number.
so, if i'm putting a spreadsheet together for this calculation, i should have an if...then statement that "if f'nt is > 90 ksi, then use 90 ksi, if f'nt < 90 ksi use that smaller number.

jheidt2543:
you could use the if ... then statement in your spreadsheet, but i prefer to use the min function. it accomplishes the same thing, but i find it is easier when you need to check your work.
joel berg
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
does flexural reinforcement count for shear friction huangyhg 产品功能分析 0 2009-09-08 07:15 PM
design of anchor bolts that is tied with hair pin tie huangyhg 产品功能分析 0 2009-09-08 05:33 PM
can i count on shear-friction capacity of the reinforcemen huangyhg 产品功能分析 0 2009-09-07 10:22 PM
block shear vs. shear rupture at connections huangyhg 产品功能分析 0 2009-09-07 03:57 PM
anchor bolts in shear tension huangyhg 产品功能分析 0 2009-09-07 11:52 AM


所有的时间均为北京时间。 现在的时间是 07:37 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多