默认 honeycomb in concrete footings

honeycomb in concrete footings
hello,
i am trying to get opinions or good references for determining how bad a problem there is. a contractor poured concrete pad and strip footings. formwork was not good and the footings bowed out on the sides. once the forms were removed, there are locations that are honeycombed. any good references or issues i should look for to determine a good course of action? the building is a prefab metal building supported by piers and pad footings. thank you.

i am not familiar with any guide for this. when i encounter this, i use my engineering judgment--is the honeycombing below the neutral axis of the footing? only the concrete above the neutral axis is needed for the compression block for flexure. how bad is the honeycombing? is it bad enough to cause problems with resisting shear? if you can be comfortable the footing will still function properly, accept the honeycombing.
i have seen this more often than i would like, which is why i think low water-cement ratio is a bad thing, especially for footings. footings don't get vibrated, and if the concrete mix is too stiff, this is what you get.
daveatkins
daveatkins,
which location are you in? is it a remote part of africa? "footings don't get vibrated" is rather a scary statement.
in general i recommend having honeycombing broken out back to sound concrete. repair can either be by recasting or using a repair compound.
it is useful to keep a record of unacceptable work, maybe you can trace it back to a particular supervisor or labour gang.

i wouldn't accept, nor reject a footing without knowing the exact extent of defects. it can be a localized edge defect caused by improper vibration, or loosing mixing water (the concrete mix is too wet usually) at the dislocated form works. or it can be the concrete mix possess problems - keep adding water to maintain flo-ability thus reduces strength globally. i will have less problem to accept honeycombs on side face of wall or pedestal, which can be repaired as suggested without much adverse consequence.
collecting the testing result, record and mapping the defects (add'l tests maybe required), then talk to the eor should be the proper way to handle this.
zambo,
no need for sarcasm. here in wisconsin, on smaller footings, my understanding is that vibration is not done.
and if you are going to repair honeycombing, "breaking out to sound concrete" is improper. a concrete patch should never be feathered, so the area with the honeycombing should be cut out deep enough so a proper patch can be cast.
daveatkins
im from australia !
footings including pads and strip footings are normally not vibrated (just well spaded) and i have poured so many of these that its no joke. never had an absolute issue with them. i do agree that engineering judgement is needed on honeycombed concrete and where forms fail, it throws alot of doubt on the competence of the contractor.
the repair could be worse than the current situation.
what kind of load (magnitude and type)is on the strip footing? what kind of structure? it sounds like you have vertical columns and a wall between may have very little load on the footing, depending on the aspect ratio of the wall and connections/continuity.
if the load is not great, the footing could be vastly overdesigned dur to standard details.
on something like a simple residential footing, it is often not needed if have good soil, but the prescriptive codes require a footing, but not always reinforced, because the load is distributed and there is no flexure.
dick
zambo - perhaps you are new to the industry or from a different location (read other world).
however small building projects like this do not normally have budgets for qa/qc inspectors every hour, every day. similarly the class of builder for this work is also lacking.
engineers are not required, unless contractually obligated to oversee the construction of the work, and it is often best that they not set foot on the project thanks to a very litigous society.
if you are new, perhaps this is an eye opener and will be informative. if you are experienced, we'd rather not be subject to you sarcasm.
regards,
qshake
eng-tips forums:real solutions for real problems really quick.

apologies for the sarcasm.
i think the opinions must indicate an industry difference. i usually work on international standard infrastructure projects - including in africa.
we always ensure all structural concrete is compacted. this can either be by vibrating or by specifiying a self-compacting mix. one of the points is that the design would assume the concrete monolithic and not honeycombed.
we do not however compact lean concrete which is being used to form a level area for the later casting of structural
back to the original post. the first step is to determine how serious the problem is:
1. are the pad and strip footings reinforced concrete?
2. if they are rc is the rebar now visible?
3. are there any anchor bolts cast into the pad footings?
4. if there are anchor bolts is it possible that the honeycombing extends to a zone around the anchor bolts?
if the concrete is not reinforced and anchor bolts are not present, or not affected, then i agree that there may be a less extensive rectification possible rather than my earlier advice to break back to sound concrete and then recast or repair.
if rebar is visible, or the cover to the rebar is sufficiently reduced to affect the durability i think there is no option other than an effective repair.
if the honeycombing could affect a zone around anchor bolts then further investigation should be carried out. anchor bolts are often at maximum loading during erection of the building and poor quality concrete could cause a failure.
thank you for all the responses. my computer has been down until today and this is my first chance to get back online. the strip footings are lightly loaded. the building frame is supported by the pad footings. they are oversized for uplift. the rebar in the footings is not exposed and has proper cover. after thinking on it further (all weekend unfortunately), i am not discovering a good reason to reject the footings. the honeycombing is at the edges that blew out, poor workmanship. they did not do a good job on this and it raises quality issues down the line. the same contractor will be doing the piers and floor slab. a preconstruction meeting prior to the slab and pier construction is already scheduled to reiterate what is expected. thanks again for the responses, this site is most helpful.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
concrete sampling guidlines huangyhg 产品功能分析 0 2009-09-08 12:34 PM
concrete roof slab load huangyhg 产品功能分析 0 2009-09-08 12:34 PM
concrete mix= reinfocing for exterior composit deck huangyhg 产品功能分析 0 2009-09-08 12:19 PM
concrete corrosion in partial saturated condition huangyhg 产品功能分析 0 2009-09-08 11:54 AM
chapter 4 preliminary design properties of concrete huangyhg 产品功能分析 0 2009-09-07 11:23 PM


所有的时间均为北京时间。 现在的时间是 09:51 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多