默认 guy wires for a stainless steel chimney

guy wires for a stainless steel chimney
i am looking at a project in which some existing stainless steel chimneys are projecting 25 ft above a roof. the chimneys are for some summer boilers, and the client figures the exhaust may be around 800 degrees f. they have requested that we look at the possiblility of extending the existing chimneys another 20 feet.
during a site visit, i noticed that the existing guy wire support brackets have pulled upwards and have lifted the lag screws out of the parapet. i am concerned about the thermal expansion of the stack (i believe that's what caused the failed brackets, not wind loads).
the existing guy wires have an adjustable threaded turnbuckle at the bottom to allow for tightening. i'm wondering if there are some spring loaded connections available to allow the pipe stack to move upwards, but still maintain some tension in the wires when the boilers are not operating?
re
"to my knowledge, you won't be able to get away from this using guy wires."
no, his suggestion of using springs, preferably travel limited, is entirely sensible.
cheers
greg locock
karlt stated:
"during a site visit, i noticed that the existing guy wire support brackets have pulled upwards and have lifted the lag screws out of the parapet. i am concerned about the thermal expansion of the stack (i believe that's what caused the failed brackets, not wind loads)."
while using springs to aid in restraining the stack is a viable option, the increased loads due to thermal expansion wil not go away. the supports must be designed to accomodate this and he is clearly already concerned on the ability of this connection to transfer forces.
newton's third law:
for every action, there is an equal and opposite reaction.
hi karlt,
another take on this, calculate the force required to restrain this thermal expansion and design a new connection at the parapets and guys if necessary.
you will probably need to redesign anyway as you have been asked to look into extending the stack. the possibility of having another level of guys due to the natural frequency of the new stack also exists.
regards
vod
i think i may have caused a bit of confusion with my post. the original brackets failed because they were overloaded by the guy wires. i am guessing that the guy wires were all pre-tensioned. then when the boiler fired up and the stack eleongated upwards, the guy wires stretched and the weak link in the chain was the connection, which gave way to relieve the build-up of stresses.
i guess my thought was that if the guy wire was pretensioned and then the wire had to elongate an additional amount, then that amount of elongation may break the guy wire. (delta = pl/ae, p may become greater than pultimate).
if a spring is installed in the system, then my thought was that the delta is taken up by the spring, and the guy wire no longer elongates. however, i guess what chipb is saying is that the tension in the guy wire will still increase, since it is still part of the overall system?
karlt;
i don't know if you have the room, but if you can move the guy rope connection location further away from the stack it will help reduce the expansion load on the ropes. in other words try to make the guy ropes more horizontial.
karlt,
correct. the use of the springs will aid in the reduction of the thermal loads by decreasing the strain in the cable by the amount the sprong compresses, however, you'll still get an increase at the connections.
you can calculate the amount of vertical thermal growth at the guy wire connection if the wire wasn't there, then, using the guy wire angle, calculate the vertical component of your pl/ea of your wire, and model it in as a spring support, and figure out the overall strain and force in the guy wire.
typically, guys for these types of structures require some initial tension. make sure you account for this.
regards
vod
karit
i would suggest you to modify the connection at guy wire support. to allow elongation, you can make a slot so that guy wire can adjust its length by sliding in the slot. during normal operation, when the temp. will be high, the guy support will shift closer to the chimney. but in shutdown condition, there should be a spring to pull the support back to its original position.
regards,
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
design of stainless steel pipe under concrete tank huangyhg 产品功能分析 0 2009-09-08 05:51 PM
connection of structural steel with stainless steel huangyhg 产品功能分析 0 2009-09-08 01:15 PM
brick masonary chimney for coke oven plan huangyhg 产品功能分析 0 2009-09-07 04:51 PM
astm steel grade to support basement wall huangyhg 产品功能分析 0 2009-09-07 01:47 PM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM


所有的时间均为北京时间。 现在的时间是 09:19 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多