so, without telling anyone, contractor decided to substitute fiber reinforced concrete instead of the vulcraft metal deck with concrete/6x6wwf i spec'd for a second floor. now he calls, wanting approval from yours truly so the job can proceed. i checked with vulcraft to see if the frc is an acceptable substitute, and they (understandably) have no position either way.
anyone run into this scenario before?
is the steel deck composite or non-composite deck?
non composite
manofstl,
looking beyond the obvious contractor issues you are facing, the use of steel fibers is adequate as a substitute of wwf for temperature and shrinkage reinforcing according to the may 2003 update to the steel deck institute' design guide.
"cold-drawn steel fibers meeting the criteria of astm a820, at a minimum addition rate of 25 lb/cu yd (14.8 kg/cu meter) and possessing an average residual strength of at least 80 psi (550 kpa) when tested in accordance with astm c1399, may be used as a suitable alternative to the welded wire fabric specified for temperature and shrinkage reinforcement"
if it was composite deck i would be less concerned, but as you see in the vulcraft manual, there are minimum areas of steel that are required and notes regarding when the mesh should be draped for non-composite deck.
i've never heard anything good about substituting fibers for mesh. my understanding has been to count on fibers (particularly synthetic fibers) only for increasing the aesthetic value of a slab.
steel fibers work great for temperature and shrinkage reinforcing especially for slab on grade. this is not a suprise considering that most anyone who has seen where the wwf actually ends up in almost all placements (on the bottom of the slab). i would not spec it, nor is it code approved for, a replacement for required flexural reinforcing.
my previous post is valid (as the sdi document states) for composite slabs only.
a lot depends on the reason for specifying wwf. willisv has a good reference for temperature and shrinkage. another resource, if the wwf was for structural purposes, is the wire reinforcement institute at
just check your deck design for non-composite capacity carrying the concrete. many vulcraft non-composite tables are based on using the wwf for actual concrete reinforcing. if the new use of the form deck without reinforcing is ok per the tables then the fibers may be ok structurally as the deck simply takes all the structural loading and the concrete is just a mass going along for the ride.
if the deck by itself can't take the loads without the wwf reinforcing, then you've got a problem...or rather, the contractor has a problem.
well, vulcraft's manual doesn't call it out, however, another metal deck company (csi) states in their fine print, something about reducing the tabulated loads by 10% if wwf per aci isn't used for their composite deck. to me, that implies it is essential in form deck.
chipb - how does a note about composite deck imply anything about non-composite form deck?
if there were any cylinders poured with the steel fiber mix, maybe you could use those tensile test results (steel fiber doesn't help that much in compression) to check the design of the concrete (assuming that the deck does not support anything, structurally). i have read that adding 1.5% (by volume) of steel fibers to concrete mix can increase tensile strength up to 40% and flexural strength up to %150.
if there were no cylinders poured, but you knew the type of fibers used and the amount, you could possibly determine a ball-park strength of the concrete and use those numbers to check the design.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
fiber reinforcement in residential slabs huangyhg 产品功能分析 0 2009-09-09 11:36 AM
fiber reinforced concrete huangyhg 产品功能分析 0 2009-09-09 11:36 AM
fiber reinforced concrete replace wire mesh huangyhg 产品功能分析 0 2009-09-09 11:35 AM
carbon fiber retrofitting huangyhg 产品功能分析 0 2009-09-07 10:56 PM
carbon fiber reinforced precast panels huangyhg 产品功能分析 0 2009-09-07 10:56 PM


所有的时间均为北京时间。 现在的时间是 07:26 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多