几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量  


返回   几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量 » 三维空间:产品设计或CAX软件使用 » CAD设计 » 产品功能分析
用户名
密码
注册 帮助 会员 日历 银行 搜索 今日新帖 标记论坛为已读


 
 
主题工具 搜索本主题 显示模式
旧 2009-09-08, 11:48 AM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 concrete clarifier help

concrete clarifier help
i am designing a 180' diameter concrete clarifier and i have some problems to work out. does anyone design concrete clarifiers out there?
1) i read aci 3502-04 and it suggests using a membrane slab with no construction joints. i think that is impossible for a 180 diameter clarifier. that is 472 yars of concrete. i would prefer to use radial construction joints at 30' on center with an expansion joint at radius = 60'.
2) my other problem is vertical construction joints in the wall. do i weaken the plane at the construction joint by decreasing the section (sawing or forming a joint), seal it, and provide a water stop or do i just provide a waterstop without weakening the plane at the construction joint? is it better to use a vertical key or dowels at the construction joint to trasfer the out of plane shear?
3) how do i calculate the base shear due to thermal expansion outwards so the wall does not slide off of the slab?
check out our whitepaper library.
you need to, quick like a bunny, buy, borrow or steal "circular concrete tanks without prestressing" from the portland cement association (pca).
1) if that's what they say, they're wrong.
2) you need to provide construction joints in the wall with waterstop that align with the construction joints in the slab. no weakening is necessary, unless you want to chamfer the joint.
3) the wall should be supported by the slab via dowels. you'll need to transfer the out of plane shear and bending moment through these dowels. once this is done, the thermal shouldn't be a problem.
it would be a good idea to find an existing clarifier and look at the details. everyone's look pretty much the same. if you don't have typical construction joints with waterstops, take a look at those also. i'd send you ours, but i don't know if my bosses would appreciate it. but usually the municipal designs are pretty much an open book and you can review those for ideas.
i have pca circular tanks. pca doesn't give much guidance on slab design. nothing does. i get conflicting information from every source. i have the new aci environmental 350 series. they talk about membrane slabs. i think membrane slabs are fine for a small clarifier but 180'diameter... i have some existing drawings for clarifiers just not any with a diamter of 180'. what about expansion joints in the slab?
anyway, what are we doing at work on saturday???!!!
another question.
i've seen toes and heals (like retaining walls) at the bases of walls of clarifiers and tanks and i have not seen toes. i don't know how the tanks and clarifiers without toes are tranfering the base moment into the soil. there is a base moment at the bottom of the wall much like a retaining wall. i just design the base slab at the wall like a retaining wall. can anyone explain how the walls without toes deal with that base moment?
the slab needs to be thick enough under the wall to carry the moment from the wall. as a rule of thumb, i make it 3 inches thicker than the wall. it needs to be wide enough to distribute that moment and vertical load to the soil below. plus you'll need to put circumferential reinforcing in the slab under the wall to carry the shear (table a-12 in pca)from the base of the wall. this isn't explained very well in the pca reference.
use the pinned case to design the wall horizontal steel and the fixed case to design the wall verticals.
the heel (beyond the wall) is handy to put in the circumferential reinforcing, add hooks to the radial steel and for overturning. as a minimum, i'd put in a heel length as thick as the wall.
i like to do an overturning type calculation with the calculated moment from pca on just the thickened slab portion. note that the liquid in the tank can resist this overturning. beyond the thickened portion, you can reduce the slab thickness to about 8 inches and use the "membrane" slab as mentioned in aci 350.
as far as being in on a saturday, i got to keep ahead of you guys who are learning to design clarifiers.
i don't understand the circumferential steel to take the shear. i use dowels in shear friction to transfer the shear into the footing much like the "d" bars in the crsi retaining wall. i also use a bigger heel to help resist the "overturning". i treat it as a retaining wall with the base moment. my toe can get to be 3' wide. is this a proper approach?
if the toe is the portion that goes into the tank, 3'-0" is reasonable. i usually use more due to the layout of the tank.
as far as the circumferential steel in the slab, you need to multiply the shear from table a-12 by pi times the radius to get a total force. it's similar to a pressure load. design the slab steel for this force. the easiest way to picture this is that it's the difference between the pure pipe stress and the stress obtained from tables a-1 through a-11. as you'll notice, the stresses drop down to nearly nothing at the bottom of walls. if you look at figure 10, you'll see a illustration of this effect. these stresses need to go somewhere.
no,
i'm saying that the toe is on the exterior of the tank and the heel is on the water side. when i am checking overturning, i look for a factor of safety greater than 1.5. but i also check the soil bearing pressures for overturning using a retaining wall model much like the retaining wall examples in crsi. i use the base moment at the base of the wall as the overturning moment. i then calculate resistance and bearing pressures using the toe (outside of the tank) and a portion of the tank slab (the heel) to resist the overturning moment, weight of the wall and water over the heel. i find it difficult as times to keep the bearing pressures within allowables if the tank wall is high. is my methodology correct?
"there is a base moment at the bottom of the wall much like a retaining wall."
i'm not familiar with the specific construction here. but a cylindrical shell filled with liquid resists the outward force of that liquid by hoop tension in the shell, not by being cantilevered up from the ground. also, a cylindrical shell can resist some degree of uniform rolling moment applied to the end- see "formulas for stress and strain", for example.
jstephen, there is a moment at the base.
vincentpa, as long as you're using unfactored loads, it sounds like you're doing it right. but i usually don't have an overturning issue. if you extend the heel (by thickening) so that more water can be used to resist your overturning it will shorten your toe. plus you have more weight in your heel.
i agree with all of the above, except that the pca reference gives charts for designing the wall as fixed or hinged at the base, so there can indeed be zero moment at the base. so, jstephen is also correct.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
chapter 4 preliminary design properties of concrete huangyhg 产品功能分析 0 2009-09-07 11:23 PM
blinding concrete - specified grade huangyhg 产品功能分析 0 2009-09-07 03:56 PM
30mpa parking garage concrete slab vs. 35mpa huangyhg 产品功能分析 0 2009-09-07 08:39 AM
3000 psi concrete requiremen huangyhg 产品功能分析 0 2009-09-07 08:39 AM
28 day vs. 56 day concrete breaks huangyhg 产品功能分析 0 2009-09-07 08:34 AM


所有的时间均为北京时间。 现在的时间是 08:56 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多