默认 5 to 8 air entrainmen

5 to 8% air entrainment
if i am desiging a 100 feet long and 2 feet high retaining wall with 5 to 8% air entrained concrete for freezing and thawing, do i still need contraction joint?
the number of joints have nothing to do with air entrainment. it has to do with the amount of shrinkage and the amount of horizontal steel to resist the shrinkage forces.
with normal amounts of steel, i would recommend contraction joints at about 25 feet.
i agree with jike, but in my experience, cracks form about every 10 ft in low retaining walls if a footing is cast first, then the wall. if you want to control this cracking, space the joints at 10 ft centres.
joints (ftng. matching wall) at 10 ft spacing sounds great to control (appearance) the cracks. i would also include a few 3/4" expansion joints (dowels w/end cap) to give your ret. wall a little room to move.
i didn't mean joints in the footing at 10' centres. just in the wall. the footing doesn't shrink as much as the wall, but does it earlier. who cares about cracks in the footing, you can't see them.
i will mention an additional criteria that is for low walls only: the spacing of joints should not exceed about 3 times the height of the wall. this corresponds a little closer to hokie66 (for low walls).
thank you guys. what would i do with out you?
by the way if the contractor does not pour this whole 100 feet long wall in one pour and does it in the stages with construction joints so than we will not need any contraction joint as there isn't a large chunk of concrete setting at any given time?

i did not read your original post thoroughly. a wall only 2 feet high is like a curb. 10 foot spacing makes sense.
i would still insist on 10 foot spacing for contraction joints but the contractor may substitute a construction joint for any contraction joint. provide an expansion joint at 20 foot spacing.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
i-6al-4v bleed air duc huangyhg 精密机械 0 2009-09-06 09:31 AM
air purification huangyhg 精密机械 0 2009-09-05 10:16 PM
air force engineer huangyhg 精密机械 0 2009-09-05 10:16 PM
air flow in a pipe huangyhg 精密机械 0 2009-09-05 10:16 PM
air conditioning huangyhg 精密机械 0 2009-09-05 10:15 PM


所有的时间均为北京时间。 现在的时间是 08:41 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多