默认 wind load calculation for belt conveyor truss design

wind load calculation for belt conveyor truss design
i am designing some standard conveyor belt trusses. i got all the belt details, carry & return idler details, material loading etc. however, i am looking for any good reference for wind load calculation. the trusses, walk ways, cable trays, service pipes etc all have contribution in wind loading. again, adding their effect individually may lead to unrealistically high wind load. also, wind load profile on belt profile itself is subject of further study! probably specific wind tunnel test results with all the ancilliaries will predict appropriate drag coefficient. unfortunately i do not have such data available to me. i am wondering if there is any good reference available for wind load calculation for this type of structures. i am following australian standard for wind loading but i failed to find any good guidance in this matter. any help will benefit me! thank you all in advance.
am
find a job or post a job opening
you鈥檙e correct to assume that wind load will be applicable to the truss/walkway steelwork, belt , piping and cable tray.
for wind load on the steelwork, use as1170.2 clause e2.3 鈥淢ultiple open frames鈥?or section e4 鈥淟attice towers鈥? some design guidelines simplify this by making the following assumptions: terrain category 2, wind acting 15m above the ground and drag coefficient of 2.0 on all steel sections. for wind load on the belt, assume vertical profile of 0.5m. for wind load on the piping and cable trays, as per as1170.2.
a 鈥榮hutdown鈥?windspeed of 20m/s (or more) may be appropriate for combination of wind loads with dead loads, maximum walkway live load and normal or flooded-belt material load. refer to as4324.1 鈥淢obile equipment for continuous handling of bulk materials鈥?for more information on this. the ultimate wind load may only be applicable for the 鈥?.2g + wu鈥?and 鈥?.9g + wu鈥?combinations.
the worst combination of gravity loads (dead load, walkway live load and flooded-belt material load) is usually the design case for the chords and the vertical struts and ties. the wind load will influence selection of the horizontal struts and ties and may only slightly influence the chord size.
dbuzz
thank you for your input. i am glad that i am on the right track. i did not consult as4324.1 yet but will do.
best regards
am
is there a possibility that the owner may want to hang siding on the conveyor bridge in the future? for instance, to keep rain or snow out. you might want to consider that and design for a wind load not less than on the full projected area of the truss.
jike, there's not much snow to worry about in australia! for some dry materials, powders and moisture-sensitive materials there may be a corrugated light-gauge metal cover (semi-circular in section) over the belt and idlers.
am,
from what i can recall. the wind load calculation of conveyor truss has nothing very special. the load will come from:
1. wind on the truss members, the same way as you calculate the load on a 3d open web truss. if icing is present,
asce 7 98 and 02 has section and provisions to compute wind pressures on trussed and latticed structures.
many thanks to all of you for your valuable input.
however, i would still like to see if there is any document available where they have indicated the drag coefficient for carrying idler + return idler location. width, shape of carrying idler and return idler and spacing between them will have some special drag coefficient for wind load calculation.
on another token, i am wondering if there is some special requirement to be satisfied with respect to the natural frequency of the conveyor and idler rotation or belt speed.
thank you all again.
regards
am
am,
i've never seen the wind loads calculated for carry or return idlers. also, i've never seen a natural frequency check undertaken for the exitation of a conveyor truss by the belt/idlers.
have you seen a belt conveyor in operation?
am,
we once had a situation, (before i worked here) where we had a large stacking conveyor that was carrying very large rip-rap, 30" minus along a conveyor at 200 ft/min. the stacker was configured like a guyed pole, cables slung from a single point to support the truss. to make a long story short we ended up with a fatigue failure on a plate due to the slow cycling of heavy rock bouncing over idlers. this is the closest thing i have ever encountered that would be considered a dynamic failure. typically aggregate particals are small and travel fast. this makes them act as a uniform distributed load, and any dynamic effects can be absorbed by impact factors. cema has impact factors given in their 5th edition which work well (table 5-6). you can certainly calculate the frequency of the load as it is proportional to the belt speed and the idler spacing. typically dynamic (time-history) analysis's account for peak or spike loads, and the response of the structure some period of time after that. i can't see how you could analyze the structure dynamically for a continuously cyclic load, especially since the load continuously varies (feed is typically not perfect). typical practice in the industry is to design for uniform load, and the worst case of surcharged belt load, and the load calculated based on the belt speed and average tons per hour, multiplied by the impact factor. only occasionally will the second method control.
dbuzz
my sincere apologies - i meant belt, not idlers. i understand that some company in australia undertook this study with wind tunnel test results; unfortunately i do not have copy of their report.
aagman
your explanation on time-history analysis is very helpful.
thank you all for your valuable input.
regards
am
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
using roof snow load as a design load huangyhg 产品功能分析 0 2009-09-16 05:58 PM
emporary wind loads huangyhg 产品功能分析 0 2009-09-16 01:09 PM
load combination questionpoll huangyhg 产品功能分析 0 2009-09-10 11:01 AM
design build huangyhg 产品功能分析 0 2009-09-08 05:13 PM
british wind loading codes huangyhg 产品功能分析 0 2009-09-07 05:19 PM


所有的时间均为北京时间。 现在的时间是 02:39 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多