we are installing a rooftop ac on an existing roof. we will be installing angle framework to support the unit and curb between joists which are 5' o.c. i intend to build the curb with treated wood either on top of the deck directly over the angle framework and build it up directly from the angle framework. are there any guidelines as to when it is ok to build on top of the deck so the deck is not "squashed" between the curb and support frame? maybe an allowable plf of curb perimeter? most details i have seen show the curb on top of the deck. a vulcraft deck manual was no help. an nrca manual detail shows it both placed on the deck, and directly on the support "for heavy units". deck is 22 ga type b. the unit has not been specified yet but i'm guessing it will be around a 1200 lb.
thanks in advance!
briansch
the loads you have should not be significant enough to affect a 22 ga. deck. assuming a 16-foot perimeter for the angle frame and nailer, that would yield a load on the deck of 75 lbs/ft, or less than would be experienced with typical foot traffic on the deck.
as an example of a higher load, a "hot" lugger for roofing with 15 gallons of asphalt weighs about 175 lbs, and with two wheels, exerts a load of almost 90 lbs and a contact area of about 4 square inches.
thanks for the response, ron.
briansch
vbridge (visitor)5 apr 02 11:23
the load contributed to the roof deck is likely going to be 300-400# concetrated load at each corner of the rtu. you might want to check with the cut sheet of the rtu. the cut sheet will show you the distributed load or the manufacturer should be able to tell you the likely load distribution.
when supporting a rtu on metal deck, what i normally do is providing steel channels under the unit. but, for lighter units, i.e. 150#-350#, i would provide 2x's inside the deck flutes to keep the deck from crushing.
sdi/steel deck manuf. normally recommends a 250# max. concentrated load on the deck.
check out:
jae...good link, thanks! consistent with my experience.... not an issue.
i'm starting to worry about you...you come up with some of the most obscure, yet relevant links. how do you do it?
thanks, vbridge and jae. jae, that was a very good link! it was exactly the information i was looking for.
briansch
try
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
roof deck lateral buckling huangyhg 产品功能分析 0 2009-09-15 07:18 PM
lateral load resistance of slab on metal deck huangyhg 产品功能分析 0 2009-09-10 09:42 AM
exceeding maximum unsupported span of metal deck huangyhg 产品功能分析 0 2009-09-09 08:47 AM
doubling steel deck for increased strength huangyhg 产品功能分析 0 2009-09-08 07:27 PM
b roof deck vs c floor deck - for floor use huangyhg 产品功能分析 0 2009-09-07 02:07 PM


所有的时间均为北京时间。 现在的时间是 12:28 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多