默认 minimum composite deck thickness

minimum composite deck thickness
just looking for a rule of thumb for a typical 100psf corridor commercial application. what is the minimum concrete thickness above the deck you like to use? when there's only 2" of concrete above the flutes i kinda get worried because i've been told by other engineers not to go below 2 1/2". wondering if it is a valid point. obviously vulcraft isnt going to list a product that wont work, but.....
check out our whitepaper library.
concrete thickness over deck and whether to use hard rock or lightweight concrete is driven by the required fire rating.
no rating is reqired. would you use the thinnest deck?
i have found that when fire rating is not a consideration then often the thickness is controled by the need to provide sufficient mass to minimze transient vibrations. i do not recommend less than 2 1/2". i often use 3 1/2" to control vibration. if you have composite beams with headed shear studs, you need a minimum stud height above the top of the deck of 1 1/2" plus perhaps 3/4 to 1" of cover.
i also agree with jike on the vibration issue with thinner decks. verco catalog has span tables for 2" over metal deck (for example, 4" total thickness for w2 and 5" total thickness for w3 deck).
one question: is stud length of 1 1/2" minimum above the top of deck required by code?
aisc manual of steel construction, chapter i, section 5.1.4 (page 5-60 of the green asd manual) requires the stud length to be 1 1/2 above the top of the metal deck.
also, total slab thickness shall not be less than 2" above the top of the deck. i.5.1.5.
if the slab is too thin (say 2"), it will often produce a hollow sound which gives a "cheap" feel to the building rather than a solid feel.
jike:
i agree. i was giving the code miminums above (at least the aisc minimums). in the absence of a required fire rating, i usually use 3" above the deck, just for that reason, and vibration control.
thank you for the code reference. i also would not use a 2" over deck for the reasons you mention. but if one was to use 2" over deck profile (as per deck manufacturers' catalogs) is it acceptable to design beams/girders as non-composite?
another reason to use a thicker concrete is for installation of expansion anchors at hanger supports. many product icc reports require 3 1/4" minimum over deck.
what process do you use to check for vibration of the deck itself? i know how to use the aisc design guide for the steel, but never for the deck.
whyun:
imho, it is should be acceptable to design steel beams and girders as non-composite if that fits the particular application better. a local steel erector has told me that if you have approximately 500 or less studs on a job, the savings in steel using compsite action probably does not pay for bringing in the stud welder machine, getting it calibrated for the job, and having the special inspector doing ring and bend tests. so, for small buildings, we tend to go with non-composite beams if we can.
good point about the expansion anchors, though be carefull of expansion anchors in an overhead application.
loui1: good question. i've always checked the entire 'system' ( beams, girders, deck, etc). never the indivual elements.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
lateral load resistance of slab on metal deck huangyhg 产品功能分析 0 2009-09-10 09:42 AM
exceeding maximum unsupported span of metal deck huangyhg 产品功能分析 0 2009-09-09 08:47 AM
doubling steel deck for increased strength huangyhg 产品功能分析 0 2009-09-08 07:27 PM
control joints in composite deck huangyhg 产品功能分析 0 2009-09-08 01:45 PM
b roof deck vs c floor deck - for floor use huangyhg 产品功能分析 0 2009-09-07 02:07 PM


所有的时间均为北京时间。 现在的时间是 10:56 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多