默认 storage barn made out of shipping containers

storage barn made out of shipping containers
a friend is builing a storage shed using stacked shipping containers welded together with a trussed roof attached.
the structure is 5' from a small convetially framed office building. the plans examiner wants a 3 hour fire rating due to the distance between buildings and their classifications.
does any one know what the fire rating of an empty shipping container is? (standard 20' and 40' containers are being used)
may be a spray on insulation would work for both the containers and roof.
thanks in advance.
david
find a job or post a job opening
are these the steel containers that you see on ships all over world? i would think the steel wall would hold up to a 3 hour fire. then you have the other wall of the same container.
richard a. cornelius, p.e.
richard,
these are steel containers.
thanks for your help.
consider cantacting the container (triwall) manufacturer.
i ams sorry. i would have never thought that a storage shed required a fire rating.
i learned something new today.
is there a minimum size before a storate shed requires a fire rating?
one more thought. can you move the shed to 10' from the building, or whatever distance before the fire rating becomes a non-issue?
we are dealing here with several plan-check related issues which include inter-alia:
1. ocupancy classification...see ibc sec 311 s-1 or s-2 for storage...could plan checker have designated one of the h(harzadous) occupancies listed in sec 307?
2. type of construction. does it have to be non-combustible or is combustible permitted? this will depend on area, height etc tables 503 and 601..seems v-b will work. note that table 601 indicates required fire ratings for building elements. read applicable footnotes in table 601 then move on to table 602.
3. location of property..table 602 <5ft..and h occupancy requires 3h, s-1 2h and s-2 1 h. the distance is 1/2 distance between exterior walls of both occupancies..i.e 2.5 ft
4. roof: in addition to table 601 check sec 1505
5. compliance to chapter 7 fire-resistance-rated construction. now for argument sake let's say 3 h is required for walls. a prescriptive approach allows for compliance with table 720.1(2). alternately compliance can be achieved through procedures of sec 721 or with research report. will an approved fire-proofing product work with what you have from a compliance stand point?
interesting problem.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
caddetails of iso shipping containers huangyhg 产品功能分析 0 2009-09-07 06:06 PM
appropriate live load for file cabinet storage room huangyhg 产品功能分析 0 2009-09-07 12:36 PM


所有的时间均为北京时间。 现在的时间是 08:54 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多