默认 post-installed anchors

post-installed anchors
i have a general question for everyone regarding post-installed anchors. we just had a brief discussion at my office regarding this, but i wanted to get others opinions.
when designing post installed anchors, do you generally use the capcaities provided in the hilti/powers manual or do you follow apendix d of aci 318?
it was mentioned in the discussion this morning that the hilti/powers manuals are vastly under-conservative when compared with values obtained using appendix d of aci 318. hilti apparently has software called profus (i think i spelled that correctly), which takes appendix d into account when arriving at capacities.
i have used the capacities in the manuals and applied my own factor of safety, usually around 10 (depending on the application) for critical components.
how do all of you approach this?
find a job or post a job opening
from what i have learned over the past 5 years using the appendix d - formerly in another document, the values from hilti, simpson, etc. cannot be compared directly. i have always used the manufacturer test values if available. i know simpson and i think hilti have a couple of anchors that can be used in cracked concrete.
when using appendix d, you have to use the coefficients that the manufacturers give you, but there aren't too many anchors out there that fall into this category.
i use appendix d, for anchor bolts and headed studs. i use the manufacturer catalogs/programs for the others.
from a presentation i attended last month, simpson, and i assume hilti, are preparing new editions of their product reports for use with aci 318-05.
with the appendix d design model, you must consider cracked concrete in most cases. as such, only a few post installed anchors are acceptable for use.
simpson has seminars to help explain (the guy in ga really does provide a non biased technical presentation), aci has seminars and so on. it really does seem to be a big step from what has been the status quo.
expect some changes.
good luck!
daniel
for manufactured post-installed anchors, i use the test report values that is adopted by the jurisdiction. traditionally, the code shear and tensile capacities for embedded anchors were much smaller than the test report allowable values for post-installed anchors with comparable diameter and embedment. though i haven't used appendix d enough to get the "feel", i anticipate similar.
i agree with rgerk to use appendix d for embedded bolts and test report values for proprietary post installed anchors (expansion anchor, adhesive anchor, shot-pin, screw anchor, etc).
be aware that if you use icc reports (icbo reports) for manufactures values, as of january 1st of 2007, all icc reports for mechanical anchors that are not approved for the new criteria of aci 318 app. d have been canceled and deleted. check
am i the only one who notices a huge difference in anchor embeddment requirements when comparing an epoxy anchor to a cast-in anchor. we've had a recent project where the contractor wanted to change from a 1 1/4" epoxy anchor (power-fast by powers) with 15" embed to a cast in anchor. i calculated that they'd need to replace it with a 1 1/4" j-bolt with a 32" embeddment. not sure if appendix d is just more conservative or if epoxy anchors are just that much stronger.
j-bolts now have much less tension load compared to headed studs or a rod with a nut on the end. recalculate with a headed stud using app. d and your answer will be much more reasonable. i would estimate that j bolts are about 1/4 of the tensile load of a headed stud using the new calculation method.
are j-bolts really as poor as the formulas suggest?
i used euro standards. there's one annex dedicated to post-installed anchors. i.e. etag annex b. hilti has published capacities according to the test procedures given by the eota - european organization for technical approvals.
in profis also, there's one option is to design using etag.
for a 1-1/4 anchorbolt, a 20" headed bolt should develop the capacity of the bolt...
dik
the story goes like this straight from the mouths of the fastener manufactures and the guys as aci.
to use the proprietary post-installed fasteners such as hilti or simpson, the post-installed fasteners have to be qualified under a testing procedure which is stated in aci 318 appendix d. there were problems with the original testing procedure in aci 318-02. none of the manufacturers tested any on their products because they did not want to waste their time and money, therefore none of their porducts were qualified to use in aci 318-02. aci has since revised the testing procedures for post-installed anchors and anchor manufacuturers have started testing their anchors to qualify them for use in aci 318-05. the manufacturer has to test the anchors and submit design information for the anchors. as of today, hilti has several anchor qualified for appendix d and simpson has a couple. i am unaware of any others. the new hilti 2006 catalog has the design values for use in aci 318-05 appendix d for their anchor which are qualified. contact hilti or simpson representatives. i have a good relation with the hilti rep in pittsburgh and he is very helpful. i have an entire design binder from them.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
post tension anchors huangyhg 产品功能分析 0 2009-09-15 01:39 PM
post installed concrete anchors huangyhg 产品功能分析 0 2009-09-15 01:39 PM
deck-railing post connection huangyhg 产品功能分析 0 2009-09-08 04:37 PM
anchors set in epoxy adhesive huangyhg 产品功能分析 0 2009-09-07 12:07 PM
about post installed in concrete huangyhg 产品功能分析 0 2009-09-07 09:28 AM


所有的时间均为北京时间。 现在的时间是 03:18 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多