默认 uplift on composite concrete slab

uplift on composite concrete slab
i am desiging the roof of a solvent storage room. because i need to design for a 100psf force in the event of an explosion, there is a net uplift on the roof. i am not concerned about the deck-to-beam connection, i'll just design the welds for the uplift force. my concern is the bond between the concrete and the composite deck. are there tables that show the uplift capacity of composite decks anywhere?
thanks so much for any help you can provide.
check out our whitepaper library.
why don't you use headed studs welded to the beams?
my supervisor doesn't think it is necessary. but that was my first choice.
is there any suction on the concrete pulling away from the deck? if the explosion is below the deck, wouldn't it all be a surface pressure on the underside of the metal deck and thus, no separation? or is this an impact effect with quick displacement that would try to pop the concrete off?
i am thinking along the lines that it will be an impact-type load. the explosion is from inside the building, so yes it is below the deck.
do you just need a light wwm layer to hold the concrete down to keep it from flying free?
dik
my knowledge of blast loads is pedestrian at best, but 100 psf sounds small: these are psi type loads. moreover, i think the design philosophy is that you want the roof to be blasted off, so as to direct the explosion force upwards in lieu of sideways to reduce shrapnel effect (if it is a detached building). not an expert here...
the delamination of the concrete from the composite deck is your concern here and i do not have a good answer for that! talk to vulcraft about it, but this is a strange load case.
i agree with jike that has on the beam flange is a cheap and positive connection. an a706 das welded flat to the beam flange and lapped to rebars in the slab would also work good. these could maybe simply satisfy catenary tensile forces in lieu of a traditional flexural design (i.e. every few feet on center, wwf catenary transverse between rebar lines). the wwf might work by itself as catenary reinforcement.
you will need to assume some "sag"

all of you have some very good points. thank you for your input.
i do have wwf in the slab so the slab should "stay together." my walls are cmu, so i am thinking of using #4 l-hook bars at 2'-0" o.c. to attach the concrete deck to the sturcture.
does this seem like a reasonable solution?
anchorage to masonry should be cautioned... there was a water treatment plant in lindsay, ontario that had a roof blow off and it lifted the first course or two...
dik
cmrazik,
under uplift pressure, the metal deck doesn't act as reinforcing steel. i'm surprised that wwf is adequate to take the tensile forces at the top of the slab. are you counting on the non-composite metal deck to handle the net uplift pressure?
cmrazik, please don't be offended at all if i'm off here. i get the impression your boss took on a project involving blast loads, which is probably an area he doesn't have expertise in.
100 psf is a large live load, and is a good blanket design if you're not sure on the live loading on a typical floor. for a blast load though, which is more likely? 100 psf or 100 psi? does your boss know? do you?
i went to a seaot seminar in dallas, one of the topics was designing for blast loads. basically, what i got out of it is that the loading depends on lots of factors, none of which i'm experienced enough with to decide on my own. i'd hire an engineer who can provide you with loading from blast loads. the seminar i went to involved a talk about designing part of the airport in dallas (dfw) for blast loads. the blast engineers gave the eor forces which their walls / roof had to resist. i'm sure your project is a much smaller scale, but i'd still be hesitant to do this.
and again, if you or your boss has the experience / knowledge to do this, please don't be offended, and just ignore my uninformed post. but if it is the case that this is out of your area of expertise, don't be afraid to tell your boss you guys need help. i've read several posts on eng-tips.com involving junior engineers asked to do things out of their expertise. one was a boss left a post-tensioned slab on horrible soil for a junior engineer to design while he was gone on vacation. the consensus on here was that the junior engineer should not do the project, and wait until the boss gets back.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
how to thicken an existing concrete slab on grade huangyhg 产品功能分析 0 2009-09-09 05:54 PM
crack in old floor slab huangyhg 产品功能分析 0 2009-09-08 02:20 PM
concrete roof slab load huangyhg 产品功能分析 0 2009-09-08 12:34 PM
concrete mix= reinfocing for exterior composit deck huangyhg 产品功能分析 0 2009-09-08 12:19 PM
chapter 4 preliminary design properties of concrete huangyhg 产品功能分析 0 2009-09-07 11:23 PM


所有的时间均为北京时间。 现在的时间是 04:41 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多