默认 rebar details for concrete column-flat slab moment frame

rebar details for concrete column-flat slab moment frame
i am working on a concrete flat plate parking garage using post-tension tendons. the columns are 27' cc with a slab thickness of 7.5". this project is located in washington dc area.
traditionally, if we have beams and girders, we can design concrete frames to resist lateral loads. how about flat plate systems?
first of all, can we only use concrete columns and flat plate to resist lateral loads (seismic and wind)? we try not to design additional shear walls if possible. if it is possible, what kind of rebar details are required at columns and flat slab? is there any guidline we can follow?
thanks a lot for your help.
shear walls.
i have never done a flat plate job where the plate is used as part of the lateral load resisting system other than as a diaphragm. it could be done, but your 7.5" thickness would be suspect, depending on the number of floors in your structure.
you mentioned both "flat plate" and "flat slab". i would think that to resist lateral loads, you should be using a flat slab (with drop panels), which you will probably need at any rate to resist punching shear unless your columns are large. don't forget to check the edge and corner conditions.
load reversal due to lateral loading would require more continuous reinforcement in both top and bottom, especially in the bottom over the columns.
a quick google turned up a number of references including the following:
here is an even better link
we have used flat plates and concrete columns on a number of projects as lateral system. aci permits use of this in buildings with seismic design category c or lower. look at chapter 21 of aci-318 which includes typical details for this system. this system is classified as an intermediate moment resisting frame.
i have also done several flat-plate-moment frames. they were in lower seismic regions.
onetimedeal,
forgetting about the seismic effects, i hope you have checked your deflections "properly" for this slab. you would never get away with this thincness in australia or europe for these spans!!
i have not checked the latest aci on this but earlier versions did not have a section on moment resisting frames for pt slabs, only pt beam systems.
great information. thanks a lot for everyone.
onetimedeal,
i forgot,
if you were to do it, you would not be able to use the aci pt logic of no column/middle strips for pt flat slabs. the sway effects would still have to be confined to the logical column strip as they are for rc slabs and detailed with continuous top and bottom reinforcement.
i agree with hokie66 that you would be better off with drop panels (l/3 of span, not 4'square) for both moment transfer and punchiung shear/reversal effects.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
moment frame to slab connection huangyhg 产品功能分析 0 2009-09-10 02:56 PM
flat slabs limited edge column moment transfer huangyhg 产品功能分析 0 2009-09-09 12:25 PM
designing columns for concrete buildings huangyhg 产品功能分析 0 2009-09-08 06:12 PM
cracks in two-way flat slab huangyhg 产品功能分析 0 2009-09-08 02:29 PM
cantilever steel beam at column huangyhg 产品功能分析 0 2009-09-07 10:40 PM


所有的时间均为北京时间。 现在的时间是 08:18 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多