默认 pressure from adjacent permanent sheeting shoring

pressure from adjacent permanent sheeting & shoring
i have a dilemma that i am hoping i can get some help with. i am currently designing perimeter cantiliver retaining walls for a below-ground precast garage directly adjacent to an existing garage. the geotechnical engineer has recommended a permanent sheeting & shoring system of secant pile walls with tiebacks between the existing garage and the new garage (the new garage extends 20' below the existing). the distance between the two garages is only 5', so the proposal is to place the retaining wall directly to the face of the secant wall.
my question is when that secant pile wall deflects 1/4" to 1/2", does the cantilevered retaining wall need to be designed for the bending associated with that lateral deflection? i am trying to convince the geotech to put some sort of semi-rigid barrier between the two walls that will crush under the force of lateral deflection of the secant wall, but will be stiff enough to not crush under the concrete fluid pressure during the pouring phase. he is insistent that the secant wall is taking the bending so the structural wall does not need to be designed for it and they do this method with bridge abutment construction all the time.
another note, due to the precast system, there is ample gapping provided for lateral movement of the wall so compression forces are not induced in the double-tees.
the secant wall should deflect during construction. if it is a premenant wall, double corrosion protected tie backs, epoxy rebar if required, then the secant wall will carry the load. if it is only a tempoary wall, the new cantilever wall must carry the retained soil. in europe, they are often used as both temporary and permenant. unless you leave about 3-4 foot of gap between the secant wall and the new cantilever wall, you will not be able to strip the back forms. in which case you should consider a one sided form.
is the existing garage on piles or caissons (drilled shafts)? if not, your wall needs to support the other garage. if you use tieback anchors, you will need an easement for going under the adjacent garage. perhaps the adjacent garage needs to be underpinned in order to support the vertical lod from the adjacent garage. if so, the underpinning will still need tiebacks.
both garages are on the same property, and the secant pile wall is being designed as a permanent underpinning system. the geotechnical engineer is designing the secant pile wall to take the surcharge loads imposed by the existing garage.
my intention is to use a one-sided form and place my basement wall to the face of the secant pile wall. my concern is any movement of the secant pile wall which occurs after the placement of my adjacent structural basement wall will impose bending stresses. even though the secant pile wall is being designed to take the load from the existing garage, won't having the walls placed side by side affect induce a lateral loading on the cantilever wall? i suggested using a rigid styrofoam layer fastened to the face of the secant pile wall (which should be finished with gunnite to leave a flat surface) that would crush under any long-term deflection of the secant pile wall but this idea has been rejected.
any other thoughts?
a secant pile wall is not "underpinning." it is a very stiff retaining wall, sometimes tied back. the secant pile wall is not "under" anything. therefore, it is not underpinning. it is more like a concrete diaphragm (slurry) wall, but is less expensive.
usually, a permanent tiedback wall should be separate from the new structure in front of it. this separation prevents just the movements you are mentioning. possibly, a tiedback secant wall is stiff enough to eliminate the movement problem that has been seen with tiedback, soldier beam walls where the building foundation wall is attached to the tiedback wall.
often, parking garages need to be open enough to allow ventilation. perhaps, you can have an opening or space between the secant pile wall and the garage structure.
you might want to call and talk to someone from schnabel foundation company in their washington, dc office. they can guide you in the right direction.
i agree with peinc that the garage should be underpinned. although in theroy the wall can be designed to accomidate the anticipated loads by making it rigid, this does not always work. actual deflections and ground movements are not well understood. this method can work for light structures that can tollerate differential deflection. this is not the case for a parking garage. the foundations should be adequately underpinned. lateral loads may require a seperate system such as the secant wall depending on the situation.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
octagon footing base pressure huangyhg 产品功能分析 0 2009-09-10 04:53 PM
lateral to vertical pressure ratio for concrete slurry-which huangyhg 产品功能分析 0 2009-09-10 09:53 AM
at rest vs active earth pressure huangyhg 产品功能分析 0 2009-09-07 01:48 PM
added internal pressure to wind load huangyhg 产品功能分析 0 2009-09-07 10:11 AM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM


所有的时间均为北京时间。 现在的时间是 05:41 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多