默认 florida building code partially enclosed v. enclosed

florida building code: partially enclosed v. enclosed
hello structural engineers,
question on the florida building code, in the wind-debris zone (but not the high-velocity hurricane zone):
our firm is designing a 7-story office space-parking building in downtown cape coral, florida. still waiting to hear if it's exposure b or c.
the architect is planning on having all openings in the bottom 60' of the building as open (no windows) for parking levels.
do i assess "open", "partial enclosed", or "enclosed" at each story?
open is defined as the "wall" having 80% openings, which the wall does at the lower parking levels.
however if i consider the wall as the entire south face of the building (7 stories high), then it is not "open" or even "partial enclosed."
the top of the building (>60'), office space, is going to have unprotected glazing. it is more than 30' from the property line, so the fbc does not require protection.
thus, it would seem i can design the top part as "enclosed"?
or is there still a requirement that i consider the windows as breachable, and thus go to "partially enclosed?"

so, with those parameters, is the building "open", "partially enclosed" or "enclosed"?
do i evaluate each level differently?
is a "wall" just considered one-level?
thank you!
seattlemike
i would consider each level as a seperate enclosure classification depending on the openings. also, check the partially enclosed criteria, the governor just signed a bill voiding the previously allowed partially enclosed classification. if in a wind-borne debris region, the window openings have to be protected.
i deal primarily with residential however. this may not apply to commercial??
it appears that per asce 7-02, c6.5.9, pg 285, glazing above 60 ft needs to be protected as well: more exactly, we need to protect windows that are 30 ft or less above neighboring building roofs. c6.5.9 clarifies that any building roof within 1500 ft (horizontal) needs to be evaluated for that 30 ft rule.
since we can't predict future construction, it seems you'd want to protect all your windows.
also, 6.5.9.3 says (vaguely) that the building's openings need to be protected.... which apparently means all of them.
city of cape coral confirmed that they want to see all windows protected.
note that windows are typically designed for a failure rate of 8 or 9 in 1000, that is less than 1%. however, in modern buildings that are complete curtain walls, each side might have several thousand 2x4 windows in the curtain wall... and typically a few fail... so, that would make one think that any curtain wall building should be designed as partially enclosed, regardless of wind-debris area?
not sure i fully agree with you on the "since we can't predict future construction, it seems you'd want to protect all your windows."
i do agree we can't predict the future, but it seems overly conservative to account for worst case possibilities for everything we design. i design for the here and now, but i'm curious to hear what others think.
my impression was that our buildings were built for a 50-year lifetime, based on the way the wind, earthquake, and snow codes are written.
also, if you do not protect the windows, you would want to design the building as "partial enclosed." see the discussion in c6.5.11.1, pg 290, of the asce 7-02.
the city of cape coral building official was pretty adamant that all the windows be protected. also, asce 7-02, 6.5.9.3 seems to indicate all the windows need to be protected. maybe that was clarified in asce 7-05.
interesting, my impression is we design our buildings to withstand a wind event that has the probability of occuring once every 50 years. i really never thought of that as the lifespan of the building.
section 1609.1.4 of the 2006 supplement to the fbc states what you said about partially enclosed if windows are not impact resistant. i can't find my copy of asce 7-02, but asce 7-05 does not allow this, you must use impact resistant glazing (with 2 exceptions). on your project you need to comply with fbc requirements, but i would do what the building official says.
the 2006 supplement to fbc still references asce 7-02.
the 50 year reference could be just a number to give people something quantifible in their lifetime, and it may be that the snow, wind, and earthquake folk just copied each other for consistency.
but nonetheless, it envokes the concept of a duration of time for which we design, although i'm sure different folk have different ideas of what this is.
but if you pursue the duration logic, and we design for a 50 year hurricane, snow storm, or 2/3 of 2%-in-50 year earthquake, then the 60 yr event (disregarding eq) exceeds our design.
the japanese think even longer term.. i think they intend for their buildings to last 100+ years, but their exact philosophies, i am not an expert in.
thank you for the clarification on 1609.1.4 and 1609.1.4.1 in the fbc 2006. yes, we are definitely going with the impact-resistance.
note the 8-9 in 1000 reference for window failure came from dr. dorothy reed, university of washington, wind engineering professor.
seattlemike
if the lower is open, then i'd only design the lower for open conditions. some jurisdictions require that for parking, a certain portion be open... 75%-80% or whatever, else they have to design the mechanical system for full ventilation else it can be natural...
dik
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
florida building code and cable bracing huangyhg 产品功能分析 0 2009-09-09 12:54 PM
florida building code 9fbc0 2007 live loads canopy huangyhg 产品功能分析 0 2009-09-09 12:54 PM
enclosed or partially enclosed that is the question huangyhg 产品功能分析 0 2009-09-08 10:16 PM
airplane hangar enclosed or partially enclosed huangyhg 产品功能分析 0 2009-09-07 10:26 AM
ada, osha and code violations huangyhg 产品功能分析 0 2009-09-07 10:09 AM


所有的时间均为北京时间。 现在的时间是 01:43 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多