transfer slab design
hi all. i'm designing a transfer slab that is supporting 2 storey blockwork dwellings. the transfer slab is 400mm tk. and is supported by r.c walls and columns in a basement car park. i'm using finite element analysis software to design it.
i have taken the worst case loading over the complete structure. this is 1.4dl + 1.6il (as per bs8110 part 1). however, i'm wondering whether i should be looking at pattern loading. my dl is 14.2 kn/m2 including self weight. my il is 3.0kn/m2.
due to the layout of structure and unsymmetrical supports i would like to take full loading over the entire structure, and ignore pattern loading. the code does suggest that i can do this if certain conditions are met (clause 3.5.2.3). my slab does qualify for these conditions, but at the end, it suggests that all the resulting support moments be reduced by 20%, with a consequential increase in span moments. this would prove very difficult to achieve as it is the fea software that i have used.
has anybody any experience in using this clause of the code? if not, does anybody have any logical suggestions that would allow me to ignore pattern loading?
check out our whitepaper library.
since the live load is so small, compared to the dead load, then why is pattern loading such a problem?
if you absolutely need to avoid pattern loading, then perhaps increase your live load by a conservative percentage, and state so in the calculations. (hoping the plans checker will concur)
thanks falseprecision. i agree with you about the difference in the dead to the imposed loading. i was just wondering if anybody had any guidelines to go by.
from a us perspective (which probably doesn't directly apply to your situation), most us codes require pattern loading in floors if you have continuity in your framing.
if you ignore the pattern loading, you are ignoring a true-life condition. that said, as falseprecision mentioned, the actual effect of the pattern loading may not be that much...but you should make a judgement on that only if you know the true effect.
as far as redistributing moments in a finite element model, one thought would be - don't redistribute the moments, rather, calculate your final design top and bottom reinforcing that is required by the actual fea model and then re-distribute the percentage of the areas of steel...they are linearly related.
are you designing for the actual positions of the walls above and their loads as line loads or distributing it as a udl?
if they are distributed as udl's i would definitely allow for patterning of both the ll and the extra dead load from above the slab. extra dead loads are only treated as such if they are of known value and location, otherwise they are live loads.
if you are allowing for the real load positions and values i would not worry about patterning it.
how are you calculating your deflections using fem?
rapt,
dead loads of all walls are in exact, real locations, inserted as line loads. the deflections are calculated using the finite software. the software gives me the total non-linear deflections.
thanks for the good advice.
when i did something similar, i reasoned that the 20% reduction in support (hogging) moment could safely be ignored as this would lead to a conservative design. the corresponding increase of span moment is going to be less than 20% so you could conservatively create a load case 1.2x(1.4gk+1.6qk) for the design of the bottom rebar. - it worked for me...
now - 3.0kn/m2 is 1.5kn/m2 on two floors - what about roof loads? - usually 0.6kn/m2 snow plus 0.25kn/m2 access. if there are access ways to the buildings there may also be higher loads associated with these.
it is also common to find that domestic buildings are modified during their life with resulting changes in loading. even if the client is adamant that this will not occur, i'd try to ensure some spare capacity to cover this.
damo74
by non-linear do you mean they include for cracking as well as creep and shrinkage deflection effects?
rapt
yeah. it is the total deflection.
damo74,
fea is right on the borders of bs8110 guidance and therefore some engineering judgement is required. for fea on something like a transfer deck, i do one of two things:
1) draw up a checker-board on the supports, and use these as the basis of alternate loadcases. where irregular bays hinder this, i use judgement at each location to input the worst case scenario.
2) perform a risk assessment on the likelihood of pattern loading being a critical factor. in some locations or loading conditions, this may not be likely. in addition, for a transfer slab i imagine that you are already using load takedowns which are on the conservative side. this is likely to have more effect than pattern loading on the deck itself.
i would be interested to see how other uk engineers handle this area, as there are several grey areas between fea and bs8110.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
slab-on-grade w embedded rails huangyhg 产品功能分析 0 2009-09-15 11:30 PM
slab on grade problem huangyhg 产品功能分析 0 2009-09-15 11:24 PM
reinforced tank design- the slab huangyhg 产品功能分析 0 2009-09-15 05:21 PM
pt slab design - something called drop bands or slab bands huangyhg 产品功能分析 0 2009-09-15 03:17 PM
design build huangyhg 产品功能分析 0 2009-09-08 05:13 PM


所有的时间均为北京时间。 现在的时间是 01:52 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多