默认 retaining wall temp steel

retaining wall temp steel
quick question. does chapter 7.12 (aci 318) apply to all flexural members for temp and shrinkage steel? it uses 'structural slab' and says it does not apply to slabs on grade, but i wasn't sure about a cantilevered retaining wall.
thanks
check out our whitepaper library.
applies for cant. retaining wall. not for slab on grade. imho
some designers use a better quality mix, thicker slabs and closer control joints without any wwf or rebar in slabs on grade. the commentary to 7.12.1 says "the provisions of this section are intended for structural slabs only; they are not intended for soil-supported slabs on grade"
you may want to also keep in mind the minimum flexural steel (not temp stl) at the tension face for retaining walls.
temp. steel is to primarily control cracking. generally it yield an unacceptable apperance. if the cracking acn be tolerated, then you dont need the steel. however, in terms of the overall structure, the cost of the temp steel is small.
for retaining walls, i use chapter 14.3. not 7.12.
archeng59 is right for cantilever retaining walls. we use chapter 10 for flexural design and meet 14.3.3 for horizontal temp steel. section 14.1.2 specifically states to do this.
thanks for the info. i didn't see chapter 14 until now.
i believe that the requirements of 14.3 assume a joint spacing of 20 feet. however, i can't find that provision anywhere in aci 318. perhaps the 20 foot limit is just a rule of thumb.
the portland cement association (pca) handbook, building movements and joints, discusses the 20 ft joint spacing for walls with openings and 25 ft joint spacing for walls without openings. i don't recall anything in aci 318 about joint spacing, although i recall reading (don't re
aci publishes aci 350 for environmental structures (tanks). aci 350 is very similar to aci 318, but not for temp/shrinkage steel (tanks cannot leak). aci 350 article 7.12 relates the required t/s steel to length of the wall between expansion joints: 0.3% for walls under 45 ft., 0.4% for walls to 60 ft., 0.5% over 60 ft. i use this for all my walls.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
retaining wall retaining water huangyhg 产品功能分析 0 2009-09-15 06:41 PM
retaining wall failure huangyhg 产品功能分析 0 2009-09-15 06:38 PM
minimum steel reinforcement in retaining wall huangyhg 产品功能分析 0 2009-09-10 02:20 PM
in enercalc masonry wall design, what is parapet heigh huangyhg 产品功能分析 0 2009-09-09 07:17 PM
【转帖】how do i create a link to an external database yang686526 DirectDWG 0 2009-05-05 12:26 PM


所有的时间均为北京时间。 现在的时间是 11:31 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多