默认 relocated building - slab on grade becomes elevated

relocated building - slab on grade becomes elevated
we are relocating a building in which a slab on grade is going to become and elevated slab. the building mover is proposing a system of masonry piers 24" sq spaced at 4'-0" oc each way to sit the new slab on. they will grout beneath the bearings at the piers to ensure direct bearing. they said they have done this numerous of times and have had no problems during or after the move nor did they have any problems with the building officials.
we were asked to provide foundation design for the relocated building. when reading aci 318, chapter 22, specifically says that structural plain concrete shall be limited to members that are continuously supported by soil or supported by other structural members capable of providing continuous vertical support. even though the slab may be reinforced with 6x6 w1.4 w1.4 wwf, it is still considered "plain" concrete per definitions section of aci. i checked the flexural and shear capacities of the 4" sog for the 4' clear span and they are all within the limits, however the code says you can't do this.
one way is to fill the space underneath the slab with grout or a flowable fill essentially turning it back into a slab on grade, however, this would be very costly. maybe you could compact the site beneath the building and pump sand under the building since sand doesn't compact. any other ideas?
has anyone come across this? this is a commercial building (dr. office) and not a house.
any tips or advice would be appreciated.
thanks in advance

you obviously can't count on the wwf even it was indicated and installed. how about add wood joists, or steel beams, from pedestal to pedestal?
how did you determine the flexural capacity of plain concrete? what tensile strength did you assume was in the concrete. i agree with aci, can not use plain concrete for elevated slab!
why can't you pour a new, elevated slab and set the old one on top?
i guess i am surprised that it is cheaper to save a 4" sog (and all the trouble that this would seem to entail) than to just demo the existing slab and pour a new one when the building is in its new location. 4" sog is pretty cheap.
i am surprised that a 4" sog could even be relocated and the op does mention 'new slab'.
if the existing slab is being reused it would be advantageous to place as much fill as possible prior to placing the slab. i doubt that pumped sand will not compact.
tip: building movers will tell you anything.
advice: don't get involved in silly schemes.
unless this is a matt footing, which at 4" it is not, i don't see the value of saving the slab. what about any stem walls, strip or spread footings? how is the slab to separated from these if present? sounds real suspicious to me too. roundfile the idea.

mike mccann
mmc engineering
and it's not even april 1.
not that funny,
i've actually seen this more than once in florida where houses are built on slabs with thickend edges at the perimeter below a masonry wall, difficult to move without slab. they decided to put in a new road or bridge and had a bunch of reasonably decent homes in the way so they moved them. then gave me a call to look at cracking slabs and masonry walls where the slab was set on masonry piers 4' o.c. told them to fill the crawl space with flowable concrete fill.
they didn't like that answer and called another guy.
good luck
how do they move an entire slab on grade and get it properly supported during the move?
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
how to thicken an existing concrete slab on grade huangyhg 产品功能分析 0 2009-09-09 05:54 PM
grade beam detail question huangyhg 产品功能分析 0 2009-09-09 02:57 PM
effects of a load on sog and below grade huangyhg 产品功能分析 0 2009-09-08 09:45 PM
crack in old floor slab huangyhg 产品功能分析 0 2009-09-08 02:20 PM
concrete slab on grade expansion joint questions huangyhg 产品功能分析 0 2009-09-08 12:43 PM


所有的时间均为北京时间。 现在的时间是 11:37 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多