minimum 1% reinforcement for foundation column?
i am designing a foundation concrete column about 6' deep below grade for frostline reason, it will support a masonry column which will have very little load (for some art exhibition purpose). do i still need to let the concrete foundation column meet 1% minimum longitudinal reinforcement requirement?
thank a lot?
you can go down to 0.5% if you can show that the reduced section with the correct amount of steel can support the loads. you can't go below 0.5%, though. check the section with a 50% reduction in area and 1% steel (on the reduced section), if that works then you can use 0.5% on the full section.
structuraleit, thanks.
more questions: for its supported masonry column, the requirement minimum longitudinal reinforcement is only 0.25% based on bcrms, so how long should this 0.5% reinforcement in concrete foundation column extend into the supported masonry column?, if it needs to be extend a development length, then i can just use this oncrete foundation column longitudinal rebar as the masonry column longitudinal reinforcement, because the masonry column it self is only about 7' tall.
thanks.
@streit,
is the 0.5% reference in the code? i have looked for it myself previously. i was under the assumption that there was no lower limit, as long as you could prove that a column of a given cross section and reinforcing could take the load. anything above and beyond that was non-structural.
aci 318-05, section 10.8.4 talks about it. it doesn't specifically 0.5% reinforcement, but does word the section such that it is pretty clear that is the intent. it says that you can base the minimum reinforcement (i.e. 1%) on a reduced effective area, ag, not less than 1/2 the total area. 1% of 0.5ag is 0.5% of ag.
many thanks.
i don't use your design code, but if it can be designed as plain concrete there should be no lower limit on the reinforcement %.
can it be treated as plain concrete with continuous lateral support? the h/d ratio less than 3 or whatever your code allows? if so, then you may be able to put less than .5% reinforcing steel. the effect of reinforcing steel is neglected. i often use a single 15m (#5) bar in 16" dia piles.
dik
being below grade, is this column built integrally with a foundation wall? if so, per aci 318-02 (i don't have my '05 handy) 10.8.2, you can take your effective cross section as being 1-1/2" outside the tie reinforcement rather than using the full outer limits of the concrete.
it is best to use a minimum of 0.5% vertical reinforcement to resist potential frost forces. with frost adhesion on the sides of the pile or pedestal, you can develop significant tension. since you are assuming six feet for frost penetration, i assume you are in a cold region.
the distance the bars are carried into the masonry column can be nominal because there can be no tension in the masonry.
best regards,
ba
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
limits for reinforcement of compression members huangyhg 产品功能分析 0 2009-09-10 10:38 AM
existing steel column analysis huangyhg 产品功能分析 0 2009-09-09 08:59 AM
cantilever steel beam at column huangyhg 产品功能分析 0 2009-09-07 10:40 PM
another aci slender column question huangyhg 产品功能分析 0 2009-09-07 12:13 PM
4 ply - wood column 9i need help fast110 huangyhg 产品功能分析 0 2009-09-07 08:44 AM


所有的时间均为北京时间。 现在的时间是 09:03 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多