默认 bonded topping joints

bonded topping joints
with a bonded topping (1 1/2" over 4 1/2" slab), with joints cut about every 12 to 14 feet, would you expect the topping to shrink to a degree that sawcut joints filled with semi-rigid epoxy would tear?
interior slab - normal weight - bond was tested for tensile-bond limits and passed. joints about a sawblade wide.

jae...it depends on the mix design. with a 1-1/2 inch topping, it is likely that a "pump" mix was used, thus smaller aggregate, more paste required, and therefore more shrinkage. do the topping joints correspond to the primary slab joints?
just did a petrographic examination on a similar condition here locally. two-inch topping over five inch slab....so much shrinkage that debonding occurred over most of the slab. it had some construction problems as well, though.
topping joints do correspond to slab joint's locations.
pumped mix. 3/4" aggregate i believe.
i just have a hard time "seeing" a bonded topping (we bond tested the heck out of it) shrink when it is bonded to an older underlying slab.

any shrinkage in the topping will cause tensile stresses in the topping and perhaps minor cracking rather than end to end change in length. so i don't see the joint opening.
jae...is the bond still intact? do a sounding on the surface and you might find some unbonded areas.
i don't know if you've measured the joint width now relative to the saw blade width at the time of sawing, but that would give a magnitude of shrinkage.
any chance that the joint width was very small right after saw-cutting and that there was not sufficient width to get a proper sealant profile? if so, then the sealant might be giving a false indication of the joint shrinkage.
also, keepin mind that you probably measured tension bond when the failure mechanism for bond failure is going to be shear. figure the shear bond to be a small fraction of the tension bond.
could it have gotten very cold after sealing and the epoxy shrank?
nope - it is indoors - between 60 and 70 degrees.

since bonded shrinkage causes random cracking, how could the concrete remain plastic at the interface of the topping to the existing? was the topping sealed soon after the topside dried?
i imagine ron has hit on the problem with his comment about sealant profile. not sure what the filler material actually was, but two things usually make sealant joints fail: joint not clean and primed, or incorrect profile. if the depth to width ratio is too large, even very small opening of the joint can overstress the sealant.
the filler was a semi-rigid epoxy with an elongation capability of 24%. the joints were sawn joints which were, at 21 days, re-sawn and then filled with the semi-rigid epoxy.
the joints have cracked - primarily through the epoxy with only minimal bond loss between concrete and epoxy.
with 24% there isn't much room for movement - but again, since it was bonded, i would think the shrinkage ...at the joint....would be minimal. 12 ft. to 14 ft. centers on the sawn joints. so the question is basically, at 21 days of age (the underlying slab was older) would a 1 1/2" bonded topping stretch a sawn joint more than 24%? (i.e. the final joint width is 124% of the original)

one phenomenon i don't quite understand:
the joints have cracked - primarily through the epoxyfff">"fff"> & "the filler was a semi-rigid epoxy with an elongation capability of 24%fff">.
how exactly the crack looks? can you post a photo?
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
bonded floor slab 9meaning concrete slab with a concrete ove huangyhg 产品功能分析 0 2009-09-07 04:20 PM
basketball court slab on grade huangyhg 产品功能分析 0 2009-09-07 02:40 PM
【转帖】cosmosmotion disappearing joints yang686526 SolidWorks二次开发 0 2009-04-13 09:56 AM


所有的时间均为北京时间。 现在的时间是 12:31 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多