bending on anchor rods
i am doing an addition to a freezer facility. as part of providing a continuous thermal barrier. the insulation sub-contractor wants to put a 5" deep high density block under the column base plates. where i have x-braces, this would put the bolts in bending.
does anyone have any good ideas on how to transfer this lateral load (from wind) into the foundation without putting the bolts into bending?

dont put block under the base plate and insulate the whole column? you do your structural element, let them figure out how to insulate it.
never, but never question engineer's judgement
thanks coengineer
this is not an option.
there are several problems that come up that can be handled that way.
this situation i am working as a problem solver with a team and not on an island providing a service.
field install l8x8 angles to each side of the baseplate in line with the x-bracing. weld top leg to baseplate. fasten bottom leg to concrete with post-installed anchors (like screw anchors - titen hds etc). assume angles take all shear. assume anchor bolts take all uplift.

could you move the baseplate down and place the 5" of insulation above it around the column?
is there a slab?
even with the 5" below the baseplate, you still get conductivity through the bolts, right?
how big are the bolts?
maybe the previous idea would provide similar thermal break?
with 5" offset, i can't see any simple way to avoid designing for bolt bending. you could put plate stock between them on egde, but then you may as well just extend the column down.
any idea how it was done on the existing facility?
hope my comments aren't too scattered, just thinking "out loud".

existing facility was built 20+ years ago and this was not done. insualtion sub-contractor says that the structural engineer that he has worked a lot with doesn't give this a second thought.
i am goin gto look at putting the column on the concrete pier.
any steel that is in the slab or in contact with the floor insulation has to be insulated.
either bring the column down to pier, or raise pier to slightly higher than the floor, then insulate slab-column/slab-pier interface.
have you considered larger anchor bolts with a nut above and below the base plate? you will likely need a thicker base plate to handle the bending in it as well.
utility structures and highway structures are often built with the distance from the top of concrete to the bottom of the base plate equal to two to three bolt diameters.
can you add a shear key to the column and a cavity in the concrete under the insulation? then design the base plate and shear key for bending, keeping the anchor bolts for tension and compression. the shear key could have a small cross section in contact with the concrete - still a thermal contuit but perhaps a small enough one? if the shear could be in two directions, use a cross shaped key. regarding the other guy who would do it without questions, he/she was dead wrong and should be reported to the pe board (my opinion only). unless of course he/she can back it up with a technically defensible argument. don't fall for that garbage!!!
arent the bolts going to be a cold bridge anyway?
if they are willing to accept these then maybe they would be willing to accept a tube section welded to the underside of the base plate and embedded into a grouted hole. this takes out shear only.
design the bolts for bending stress and do not forget to heat the subgrade! (insulation only delays freezing.)
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
bending moment induced by shims huangyhg 产品功能分析 0 2009-09-07 03:27 PM
beam strengthening huangyhg 产品功能分析 0 2009-09-07 03:04 PM
asymmetric bending in wood roof purlins huangyhg 产品功能分析 0 2009-09-07 01:47 PM
annular bending of stiffened ring huangyhg 产品功能分析 0 2009-09-07 12:12 PM
allowable bending stress in plate huangyhg 产品功能分析 0 2009-09-07 10:52 AM


所有的时间均为北京时间。 现在的时间是 06:57 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多