默认 6x6 post strength

6"x6" post strength
help my basement may not be structurally sound. can anyone tell me how much load a 6"x 6" pressure treated post 8'in length is rated to hold? we have not been in the house long. the post is bowing slightly. the truss design estimates 30,000# on this post.
check out our whitepaper library.
most p/t wood is southern pine. assuming #2 grade, the
fc = 525 psi and e = 1.2. l/d ratio is 13
allowing for buckling, allowable compressive stress is roughly 475 psi, area is 30 sq in, so the allowable force in the post is 14,300 lb. however, if the post is a stronger grade, the strength goes up quite dramatically.
the first thing you should do is check the grade stamp.
the flexing could be due simply to drying, because it is unlikely that the house is loaded to anywhere near design load.
what species of wood? is the post framed into a wall? is the 30 kip load dead and live load? is any of this a roof load? snow load? what frames on top of the post? in any case, 30 kips is a substantial load to be supported by a 6x6 wood post.
is the construction new? how have you determined the 30,000 lb load? is the end attached to the floor? is the load centric?
timber construction manual specifies euler's formula with a safety factor of 2.727, that is;
sigma(allowable)=0.3*e/(l/d)**2
0.3*e/(l/d)**2=p/a
=p/d**2
solve for d, d=5.26" ok use d=5.5 nominal dim
checking normal stress;
sigma=p/a
=30,000/(5.5)**2
=991 psi
requires compression parallel to grain "fc" > 991
the only grade that meets this is dense select structural
aitc column tables provide a calculated load that can be supported based on column size, length, and material properties see
a 6x6 8' in height with no load duration factor and of doug fir #1 or better is good for about 28 kips. but usually bearing stresses of the beam on the post or the post on support will control.
as for your bow, i think that is due to shrinkage.
whatever has produced your bow, you should include a bending component in your calculation, which will reduce your allowable stress! don't screw around on the internet, get a contractor in right away, and maybe even a structural engineer. you're talking about a huge loss of this thing buckles.
in america, typical 6x6 pressure treated (pt) are southern yellow pine (syp). i agree with "trussdoc", bow is drying and actual loading is much less that design. (straight 6x6's are difficult to find)
i would consider just adding an additional 6x6 next to the existing post bolt the two together.
i found this link,
we have reinforced the post. thanks for your help. boo1 those charts were exactly what i was serching for. they correlated right on with trussdoc's calculations. thanks
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
28 days compressive strength of concrete in russian concrete huangyhg 产品功能分析 0 2009-09-07 08:34 AM
28 day vs. 56 day concrete breaks huangyhg 产品功能分析 0 2009-09-07 08:34 AM
1957 steel beam strength huangyhg 产品功能分析 0 2009-09-06 10:43 PM
fatigue strength of vascomax 350 huangyhg 精密机械 0 2009-09-05 10:46 PM
bolt strength reduction in shear lap joint with packer huangyhg 精密机械 0 2009-09-05 10:25 PM


所有的时间均为北京时间。 现在的时间是 01:56 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多