默认 slab of grade reinforcement coverage

slab of grade reinforcement coverage
if i am using #3 bars at 18" o.c. in my slab of grade am i required to provide 3" of cover as aci 7.7 specifies? or are concrete slab on grades a different ball game than what 7.7 covers? i wouldn't usually worry about it but i'm using it as a diaphragm so technically i suppose its a structural element. thanks
find a job or post a job opening
3" cover is required for concrete cast against soil. i would assume that your slab on grade is cast on top of a level course of compacted crushed stone and not directly on the soil.
stevegregory
aci reads "concrete cast against and permanently exposed to the earth". isn't compacted granular fill considered earth?
read the commentary.
"the condition "concrete surfaces exposed to earth or weather" refers to direct exposure to moisture changes and not just to temperature changes. slabs or thin shell soffits are not usually considered directly exposed unless subject to alternate wetting and drying..."
pretty clear to me.
sounds good. i guess i need to open my eyes. thanks
if the sog is for habitable space, a vapor retarder is needed and i usually interpret this as the concrete not being cast directly against the earth.
don phillips
aci 318 does not govern for slab on grades (1.1.6)
aci does have a publication for sogs but i do not have access to it. i do know that it was standard practice to spec a 5" slab with #4 at 12 mid depth for a very large consulting firm. this provides for only a 2" cover on bottom.
i believe the document teguci is referring to is aci 360 "design of slabs on ground." the only guidance given for placement of reinforcing within the slab is as follows:
for crack-width control - at or above mid-depth, typically 1.5" to 2" cover below the top surface of the slab.
for moment capacity - at the centroid of the tensile area of the uncracked concrete section.
if the slab is taking vertical or lateral loads from the structure then it is covered by aci-318, and as you had mentioned you are considering it to be a structural element. i would imagine you would take the 3" value for cast against earth, as a slab covered by aci-318 would be acting almost like a footing in some regards. however i am not entirely sure what the typical value would be as the slabs on grade i have encountered, as taguci mentioned, are not covered by aci-318. my guess is that since the steel reinforcement is not as critical for a sog (in many cases its sole purpose is crack control) that the cover requirements are not as stringent.
frv-
i hate to nit pick, but the commentary to 7.7 reads "slab or thin shell soffits..." (slab not slabs) which i take to apply only to soffits, as would appear consistent with the remainder of the sentence.
teguci-
2" does seem to be a common minimum cover for slabs on grade. as you mentioned slabs on grade that do not take loads from the structure are exempt from aci-318. i have not read anything that specifies a minimum cover for these slabs.
for a 4" thick slab-on-grade, it is normal to put the reinforcing at the center of the slab, wwf or rebar.
mike mccann
mmc engineering
in addition to my above post, a "fact sheet" on the wri website says the following:
"in the case of the lower layer, when the concrete slab is placed on a well-constructed base course (normally graded,
compacted and porous), many who design floors consider 1.5" of clear cover below the steel to be adequate. additional cover should not be necessary unless the governing building code requires a bottom cover of up to 3 inches."
i have provided a link to this document:
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
shear reinforcement for grade beams of slab on grade huangyhg 产品功能分析 0 2009-09-15 09:47 PM
how to thicken an existing concrete slab on grade huangyhg 产品功能分析 0 2009-09-09 05:54 PM
grade beam detail question huangyhg 产品功能分析 0 2009-09-09 02:57 PM
crack in old floor slab huangyhg 产品功能分析 0 2009-09-08 02:20 PM
concrete spec. for slab-on-grade huangyhg 产品功能分析 0 2009-09-08 12:49 PM


所有的时间均为北京时间。 现在的时间是 01:13 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多