默认 shrinkage temperature reinforcement in thick members

shrinkage & temperature reinforcement in thick members
i need some insight on the aashto lrfd bridge design specs.
section 5.10.8.2 states shrinkage & temperature reinforcement should be 0.18% of the gross sectional area for members less than 48" thick. the aashto lfd code required 0.125in² per ft of surface.
i am designing a bent cap that is 42" square. the lrfd code requires 3.18in² temp steel, while the lfd code requires only 0.44in² - this is a big difference.
the aashto lrfd commentary cites use of aci 318. in that code, the discussion is limited to slabs only (§7.12).
my inclination is to use the smaller value, but i cannot justify this decision within the limits of the lrfd code.
thanks in advance for your help!
is that per ft^2 of surface? (42/12)^2*.125=1.53 in2
even with that the answers are pretty different.
the sectional area is in square inches.
lrfd: 0.0018*(42in)^2 = 3.172in²
lfd : 0.125in²/ft * 3.5ft = 0.438in²
standard spec's requires that the steel required in flexure be at least 1.2x that of the uncracked section. this makes more since than the aci code, and the section you mentioned above is often misinterpreted by plan checkers. i usually cater to their comments, no matter how misguided.
so far as your bent cap goes, put in the extra steel, it's improbable that you will make a cost savings that is worth fussing over. can't really say since you didn't provide any particulars.
the longitudinal reinforcing bars meet the 1.2mcr strength req'mt as well as serviceability. they more than meet the s&t reinf requirements in that direction.
additional s&t reinf is needed perpendicular to the primary bars. stirrups or ties are used for both the shear and the s&t requirements.
this section of the code calls for 3.18in² per foot of length! this is equally distributed to four faces, so #4 ties at 3" or #5 ties at 4½" spacing are needed.
the minimum is not for the transverse direction.
you would get better responses from someone in the bridge engineering forum. i have not had the privelage of designing bent caps of any substantial size and have not used aashto lrfd.
think: 1) shrinkage cracks occur over large areas due to shrinkage (volume change incompatibility) there is release at corners/edges, 2) for the reinforcing to control cracking it has to have the necessary development length.
based on the above, as far as t&s in the transverse direction of your beam i would say #4@18" minimum. you may want to throw in some extra, so it looks extra nice, with very little cracking.
cheers, it's friday.
greetings, yack !
thanks for your advice. the aashto lrfd code is calling for the s&t reinforcing in each direction, distributed equally.
the #4 at 18" would provide only 0.133in² (lfd) or 0.533in² (lrfd) -- well under the required values of 0.44 or 3.18 in². yet we have used #4 at 12" for years, as standard practice.
and that's why i'm seeking help with the design code!!
i wasn't aware there was a bridge forum. thanks for pointing me there.
regards, raf
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
masonry horizontal joint reinforcemen huangyhg 产品功能分析 0 2009-09-10 12:40 PM
limits for reinforcement of compression members huangyhg 产品功能分析 0 2009-09-10 10:38 AM
chapter 4 preliminary design properties of concrete huangyhg 产品功能分析 0 2009-09-07 11:23 PM
analysis model of creep and shrinkage of a reinforced concre huangyhg 产品功能分析 0 2009-09-07 11:34 AM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM


所有的时间均为北京时间。 现在的时间是 01:35 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多