默认 shear wall problem

shear wall problem
a 6'x6' entry addition to an existing single story wood framed structure has been constructed. now i have been asked to show that this is adequate for wind loads.
here is the plan:
____________________
| |
| |
|_ _|
there are no openings on the sides; a 3' wide door occurs in the front wall (opposite the original building). walls are 8' high, 2x4@16" o.c., fully sheathed with structural panels. floor is slab on grade. code is 2006 ibc. seismic design category a.
ibc 2308.9.3 requires braced wall panels at least 48" wide at each end; i only have 18" each side of the door.
ibc 2308.9.3.1 allows 2'-8" panels; i only have 18"
ibc 2308.9.3.2 allows 16" panels, but the header must be at least 6' between panels; i would only have 3'-4" between the 16" panels.
so i give up on "conventional light frame construction"
ibc 2305.3.4 limits the aspect ratio of a shear wall pier to 3.5:1; each side of the door is 8 ft./1.5 ft. = 5.3:1
trying a perforated shear wall doesn't work: 2305.3.5.1 defines the height of the perforated shear wall segment to be the same as the shear wall pier.
assuming i could make the roof work as a diaphragm (the entry has a cathedral ceiling) to get the load back into the original building doesn't pass either鈥?ibc 2305.2.5 limits the length of a cantilevered diaphragm to 2/3 of the diaphragm width, so the maximum cantilever permitted is 4 feet; i have 6.
this is a simple wood box, with a hole in one side. there are countless "tool sheds" built to a lesser construction that have been standing for ions. it can't be this hard鈥?.help!!
jkw 05,
two thoughts:
1. try shear transfer around openings. ratio then becomes height of door / 1.5'.
2. assume the diaphragm is rigid, it will definitely meet the definition of a rigid diaphragm.
akastud
the roof diaphragm is small enough by code to cantilever back to the main structure with the proper reinforcing, without the shear walls.
in lieu of this, you could try one or two simpson strong wall panels, but they are pricey.
mike mccann
mccann engineering
thanks for your quick responses guys!
the cantilevered rigid diaphragm approach was the first thing i thought of, but then i saw the (2/3)*w maximum in section 2305.2.5 which i take as meaning i would be limited to 4 feet, not the 6 feet that i have.
aka...even just with the door height the ratio is ~4.4 (6.66'/1.5'), which exceeds the 3-1/2
i'm sure this structure works, but it seems like the most basic structures are often harder to "engineer" than the larger ones.
this is not a cantilevered diaphragm--it is an open front structure. l/w can be 1.5, and you have l/w = 1. this small diaphragm can rack the loads back to the main building, and the torsion can be resisted by the side walls.
daveatkins
jkw 05,
what dave atkins is saying and what i was implying by rigid diaphragm is not a cantilevered diaphragm, but a rigid diaghragm that with a center of rigidity and different center of mass. when you calculate the center of rigidity you will find that it ends up on the wall at the existing structure. all of the shear will go directly into the wall and there will be a net moment on the diaphragm that can be resisted by the two sidewalls.
akastud
ok dave. i see that. i was not considering using the two walls normal to the house to resist the torsion, which is possible here.
mike mccann
mccann engineering
now i see it....thanks for all your help!
jw
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
in-plane tilt wall shear reinforcing huangyhg 产品功能分析 0 2009-09-09 07:20 PM
in enercalc masonry wall design, what is parapet heigh huangyhg 产品功能分析 0 2009-09-09 07:17 PM
foundation wall 40 feet below grade huangyhg 产品功能分析 0 2009-09-09 01:38 PM
can i count on shear-friction capacity of the reinforcemen huangyhg 产品功能分析 0 2009-09-07 10:22 PM
block shear vs. shear rupture at connections huangyhg 产品功能分析 0 2009-09-07 03:57 PM


所有的时间均为北京时间。 现在的时间是 06:40 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多