notch at end of wood rafter
i have a client who wants to notch the end of three existing roof rafters (2 x 12 @ 24" oc) in an existing church, to install a kitchen range hood. the 1997 nds (section 3.2.3.3) states that a notch at the end of a bending member cannot exceed 1/4 of the depth of the member, so i told the client a 3" notch is ok. but he wants a 5" notch.
assuming the shear and bending stresses work (i think they will, but i have not checked yet), can i deviate from the nds? is there a reason for this empirical rule limiting a notch to 1/4 of the member depth?
daveatkins
wait the minute dave, i assume you are notching the tension side of the rafter (not at the support). you can only notch 1/6 of depth. you cant have a notch in the middle third of the span.
1/4 dept rule only apply if you rest the notch end on the wall or beam.
you can always beef up the notch rafter by sistering 2x next to it.
2x12 is 11.25" so theoratically also, 3" exceeds 1/4 rule. i think you should go ahead and notch it but sister similar rafter next to it.
also dave, if you do deviate from nds, for example if you notch 2x12 5" at the bottom or the top, you can just assume you are using 2x6 instead of 2x12. (11.25-5=6.25.. close enough to 2x6)
daveatkins - this quote from a usda forest products lab patent provides insight why notches are a problem for wood:
quote:
wood has relatively little strength perpendicular to the grain in comparison to its strength along the axis of its grain.
for example, a sample of douglas-fir might have parallel to-
grain tensile and compressive strengths of 15,600 and 3,470 psi respectively. but perpendicular-to-grain tensile and compressive strengths of only 360 and 340 psi, respectively.
the strength of a wooden beam in a spanning application derives from the fact that the forces experienced by the beam when loaded are primarily oriented along the grain (tension, compression and shear) with essentially no cross-grain tension.
this assumes, however, that the beam is supported underneath its ends and that the beam is of essentially uniform moss section without cuts or notches. this latter assumption may not always be true in practice. beams may be cut or notched in various places to run utilities or to fit against other structural
you mention 97 nds but 2001 nds increases the reduction of the allowable shear stress by squaring the de/d term (so you have the reduced shear area and the allowable is reduced by (de/d)squared where it used to be reduced by only de/d).
this "notch" is at the support--and it is really a tapered notch, because the rafter is sloped 3:12 (that is, the rafter is 11.25" deep over the supporting masonry bearing wall, there is a vertical 5" cut at the inside face of the wall, and there is a horizontal 22.36" cut in to the bottom of the rafter.
i like coengineer's idea--i will see how it works out. if it doesn't work, i will ask for sister rafters.
daveatkins
slideruleera has provided excellent information on this problem. in addition do a search on this site, since this topic has been covered several times before.
as houseguy has indicated the 2001 nds has reduced the allowable shear at notches. it is my understanding that change was made due to testing that showed very poor performance at notches.
i'd take rarswc's comment one step farther, instead of "probably" i'd say that you definately will need to ignore the shear capacity of the 2x12.
da your last description helps clarify, i think you are talking about a "level cut" at the bearing end of the rafter and there is no way that this can be justified without reinforcement. perhaps external stirrups or "oly log screws" could be used to provide shear reinforcement to the rafter ends.
i'm not familiar with any metal strapping that could be used as external stirrups but nmaybe someone else is. some carbonfiber products are used (generally) on larger members. anyone with experience using oly log screws for shear reinforcement? (i've used them on glulams for a similar condition (5 inch wide
thanks for all the help--especially the information on knots.
i "sistered" a 1-3/4" x 5-1/2" microllam each side of each rafter.
daveatkins
how about a steel plate on both sides of the rafters. they could be joined together with through bolts. in other words the size and geometry of such plates (on both sides) could take the shear and as one of the other guys suggested above, neglect shear capacity of the notched roof rafters altogether.
my first choice would be, though, to notch the hood. (make it work with whatever is already there)
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
抛砖引玉 yang686526 ObjectARX(VB.NET/C#) 0 2009-04-21 02:07 PM
【转帖】[原创]曲线打断于交点 yang686526 ObjectARX(VB.NET/C#) 0 2009-04-20 03:19 PM


所有的时间均为北京时间。 现在的时间是 03:52 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多