默认 new pile foundation

new pile foundation
have a situation where were modifiying an industrial building. the existing foundation consists of very large pile caps supported by timber piles, as can be seen in the attached sketch. unfortunately my new columns also supported on piles are approximately 20 to 36" away from the edge of these large pile caps. i am proposing to cut a seat in the existing pile and then cast my new pilecap. does this seem like a reasonable solution or does anybody have another solution?
calculor1 - don't even think about trying to notch the existing concrete. here are two good reasons:
1. trying to remove existing reinforced concrete with the precision shown in the sketch is virtually impossible (and trying to do so is very expensive).
2. if the existing piling are close to the edge of the slab (very likely), then creating the notch will weaken the cap directly above these existing piling.
additionally, the proposed new piling layout will apply a good portion of the new 500 kip load to the existing pile cap. it is unlikely existing piling have the reserve capacity to pickup this new load in addition to current loads.
imho, position your new piling to carry the entire 500 kip / column load, without relying on the any support from the existing pile cap. this may not be easy, but is should be possible.
connect the new pile cap to the existing pile cap by scabbling the existing pile cap (the full 3' depth) then drilling horizontal holes. rebar dowels can be epoxied into the holes.
soak the scabbled area with water (for at least 24 hours) before placing the new concrete. if this step is done correctly, the bond between the new and existing concrete is as good as, or better than a modern bonding agent.
sliderule i should clarify, the existing pile cap once supported a turbine which has since been removed, therefore the existing piles (76 of them) are no longer supporting anything other than the cap. my problem is that i need 4 piles per column, i only have 20 to 36" space between the edge of the pile cap and center of new pile cap basicly i can only place the piles eccentric to the column which i believe is a worst option than cutting a seat as shown in the sketch. btw i have 6" diameter casin with a 14"x14" bearing plate at top of casing which makes it difficult to satify pile spacing requirements. any suggestions?
calculor1 - here is a suggestion:
1. demolish the strip of the existing pile cap that covers the first row of existing timber piles (this would include the complete assumed tributary area for all of this first row).
2. cut off the the exposed timber piling in this first row below grade so that they no longer can carry any load.
3. design a new pile plan, 2 rows. the inner row will have to be spaced between the remaining, cut-off timber piling. the outer row will have a sufficient number of piling so that the load on all the new piling is "reasonably" equal.
4. note that the new pile cap can be any thickness you need, not necessarily limited to the existing 3' thickness.
5. if you want to tie the new and existing caps together, drill and dowel into the edge of the existing pile cap. this "may" not really be necessary, depending on possible lateral loading. if the two caps are tied together there could be a problems with differential settlement - that 500 kips / column is a lot.
a sketch of this suggestion is posted below.
this may seem like a lot of "extra" work... but compared to successfully cutting the proposed notch (or the consequences of not being able to do so), this suggestion is both "easy & inexpensive". there are a lot more piling, but once a pile installation mobilization has been performed, adding additional piling is usually cost effective.
if you need for me to go into details about why the notch is a really bad idea, i'll be glad too.
slideruleera, i agree with you. good answer.
very thoughtful!
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
h piles - end bearing huangyhg 产品功能分析 0 2009-09-09 03:39 PM
h pile huangyhg 产品功能分析 0 2009-09-09 03:39 PM
foundation cracking and settling huangyhg 产品功能分析 0 2009-09-09 01:24 PM
crack in foundation wall huangyhg 产品功能分析 0 2009-09-08 02:20 PM
connecting a new foundation to an existing huangyhg 产品功能分析 0 2009-09-08 01:09 PM


所有的时间均为北京时间。 现在的时间是 06:18 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多