默认 crack in stucco

crack in stucco
how do you fix an 1/8" vertical crack that runs through the stucco fa?ade around the window.

kxa...if you only want to repair the crack, then route it with a small grinder, then fill with a sealant compatible with whatever coating you are using on the stucco.
an 1/8" wide crack in stucco is unusual. you need to determine the cause of the crack. is it shrinkage? is it improper lath placement? it is improper sheathing placement?
stucco is often considered to be waterproof. it is not, particularly when you have cracks such as this. check to see that control joints are placed such that no more than 144 square feet are in any area. also, windows and doors are often used by architects as "control" joints in stucco. the window joint should be continued to the bottom termination, whether at the ground level or at a floor line joint.
post a photo and maybe i can offer a bit more.
ron
ron:
how the stucco is applied, brush, spray? does it need backing like wire mesh?
i saw houses around with it, but have never noticed joints. are the joints sealed and painted?
curious to know a little about stucco.
assuming it is applied over wood framing/sheathing, conventional stucco is applied in 3 coats...the first coat is called a scratch coat, the second is a brown coat, and the third is the finish coat. the thickness is measured excluding the finish texture.
generally, the stucco is applied onto an expanded metal lath covered substrate. my preference is to apply roofing felt over a "housewrap" covered substrate, then apply the lath separately. many prefer to use paper backed lath, but it is much more difficult to achieve proper flashing tie-in with paper backed lath.
the three layers of stucco have specific functions. the first coat, the scratch coat, is to provide the initial bond and foundation for the succeeding coats. it is also the one that should be used for primary crack mitigation, in that it is applied and then horizontally scored (scratched) so that very tight shrinkage cracks can form in the first layer. the second layer is the "brown" coat. it is called a brown coat because it should have a higher sand percentage than the scratch coat, so that less shrinkage occurs (and correspondingly less cracking) as compared to the scratch coat. the finish coat may be the same mixture as the scratch coat to provide a dense, durable surface resistant to moisture intrusion. in conventional stucco the layer thicknesses are required to be 3/8", 3/8", and 1/8" successively, to achieve a total thickness of 7/8".
one coat proprietary stucco systems do not directly meet code requirements. they slip in through the back door by the use of "evaluation reports" by code authorized testing agencies. in order for them to comply with the code, they must be approved by the building official, and they must follow, to the letter, the requirements of the evaluation report. they almost never follow those requirements!!
control joints are placed to break up the areas into sections no larger than 144 sq. ft. i often see control joints installed improperly in that they are fastened to the substrated on both sides, thus negating the movement they are supposed to accommodate.
hope this helps. i could write for the next hour on stucco and its construction problems!! i see them a lot.
kslee1000...sorry i didn't fully answer your question. most stucco is applied using a trowel. it can, and often is, applied by spraying. there are several finish techniques that use a brush to apply spatterings of stucco then use some other finish technique such as a trowel rub to achieve a knock-down finish or a rilled surface.
joints around penetrations are formed and sealed. control joints are generally not sealed. they are constructed using pre-formed control joints.
a photo would help, as would the type of construction. for example, is this traditional stucco or eifs?
in some jurisdictions stucco is synonomous (sp?) with 'synthetic stucco' and the cementitious type is difficult to come by.
not a bad link:
here are two pictures. the crack is about 1/8" wide.
is that a cementitious material... looks more like eifs? some of these products and the foam backing have very high shrinkage until they have cured properly.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
crack in old floor slab huangyhg 产品功能分析 0 2009-09-08 02:20 PM
crack in foundation wall huangyhg 产品功能分析 0 2009-09-08 02:20 PM
crack in composite floor deck huangyhg 产品功能分析 0 2009-09-08 02:20 PM
crack control huangyhg 产品功能分析 0 2009-09-08 02:19 PM
beam crack huangyhg 产品功能分析 0 2009-09-07 02:49 PM


所有的时间均为北京时间。 现在的时间是 06:09 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多