默认 concrete slab design

concrete slab design
i am a relatively new civil engineering technologist, and i was ust wondering what the best way to design a concrete roof slab supported by walls, with 3 feet of soil on top.
thanks
1. factor the loads.
2. draw the shear and moment diagrams.
3. check shear and moment.
4. check deflection (usually doesn't control with concrete).
5. check bar development lengths.
6. check cracking (bars spaced 12" oc should satisfy this).
daveatkins
the first step i would do is to go to the aci code chapter 9, table 9.5 (a, b, and c) and get a minimum thickness so that you don't have to worry about deflections. that gives you a starting point for figuring dead loads. then follow daveatkins procedure and you should be fine.
if you can avoid it, don't rely on the concrete as the waterproofing (if you require waterproofing).
i suggest that you hire a competent structural engineer to do the design for you. roof slabs carrying loads is not a simple task and there are many other issues that you need to worry about besides structural such as corrosion, moisture/water intrusion etc.
regards,
lutfi
lutfi is exactly right.....with all due respect, drf9984, i doubt you are qualified to perform such an analysis and design. if you are seeking such so as to be better prepared in dealing with engineers in your firm, then i applaud your efforts. if you are working in a firm where you are expected to put forth such a design, then that firm should re-think its mode of operation.
depending on the slab geometry, you could have a one way slab, a two way slab, or consider it as a plate. the slab to roof connection will influnece the design, simple support or integral.
check with the grey-beards in the office, see if they any "coldies", prior designs to follow.
best, tincan
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
concrete roof slab load huangyhg 产品功能分析 0 2009-09-08 12:34 PM
concrete mix= reinfocing for exterior composit deck huangyhg 产品功能分析 0 2009-09-08 12:19 PM
concrete design question huangyhg 产品功能分析 0 2009-09-08 12:00 PM
chapter 4 preliminary design properties of concrete huangyhg 产品功能分析 0 2009-09-07 11:23 PM
as3600 concrete strength for slab on ground huangyhg 产品功能分析 0 2009-09-07 12:53 PM


所有的时间均为北京时间。 现在的时间是 10:57 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多