buried tank subject to hydrostatic uplift
hi all, i'm a new member with a pretty basic design question. when designing the bottom slab of a buried tank which will be subject to uplift due to high groundwater, do i add the uplift force to the soil pressure due to gravity loads or subtract it? for example, if i have a 10 ft. by 10 ft. tank that carries a total gravity load of 100,000# i will have a design soil pressure on the bottom slab of 100,000#/100sq.ft.= 1000 psf. now, if i have a groundwater table that is 10 ft. above the bottom of my tank i will have an uplift force of 10x62.4= 624psf. will my total design load for the bottom slab be 1000psf + 624psf= 1624psf or 1000psf - 624psf= 376psf???
thanks!
1-you're gonna subtract the uplift pressure from the downward pressure and apply the net on the slab and that's gonna be 624psf
2-you've got also to check uplift resistance factor of safety=downwards total force/uplift total force and it should be equals or greater than the allowable i think it's 1.50
two different cases:
1) the tank is full. the weight of the fluid and the tank with foundation minus ten feet of water buoyancy divided by the area of the soil.
2) the tank is empty. the weight of the empty tank minus ten feet of water buoyancy must by greater than zero. if not, the tank will pop out of the ground. add thickness to the foundation or base and secure the tank against uplift with anchor rods to the foundation.
the bottom slab will see a service pressure of 1000psf. of that, some will be water pressure, and the rest will be soil pressure. if your water table is +10ft, then 624psf is water pressure, 376psf is soil pressure. if your water table drops to +5ft, then your water pressure is 312psf, your soil pressure is 688psf.
design the slab for factored loads minus the weight of the slab. include whatever load factors your code calls for. if, for instance, you're designing to aci350, you have a durability factor of 1.3, on top of a dead load factor of 1.3 and a fluid load factor of 1.7.
thanks for the replies. it appears i've been pretty conservative (ie, wrong) in my designs because i have always added the gravity and the hydrostatic loads together. in actuality, the groundwater table will fluctuate. therefore, it looks like my controlling case would be an empty tank with the maximum 10 ft. groundwater table. in this case i would have a factored design load of 1.7 x 624 plus 1.3 x 376 for a total load of 1550 psf. does everyone agree??
as jmiec has shown you, the water table level does not affect the pressure on the soil as long as the loaded tank weight is greater than the buoyant force. and re
hemifun-
nearly. forget buoyancy for the moment, and just look at the net design pressure on the slab. if your 100,000 lbs is for an empty tank, then you need to reduce your upward design pressure for the weight of the mat.
if your total gravity load of 100,000 lbs includes liquid in the tank, then you need to reduce your upward design pressure for the internal pressure on the top of the mat, in addition to the weight of the mat.
in either case, if you are designing to aci350, you need to factor your result by the durability factor of 1.3.
now, for the buoyancy issue, check out some earlier threads on this topic. you'll read a wide variety of opinions.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
回复


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
buoyancy of underground tank huangyhg 产品功能分析 0 2009-09-07 05:53 PM
baffle plate thickness for a rectangle tank huangyhg 产品功能分析 0 2009-09-07 02:09 PM
anchoring a rc tank base to rock huangyhg 产品功能分析 0 2009-09-07 12:04 PM
a column at center of tank bottom plate huangyhg 产品功能分析 0 2009-09-07 09:03 AM
8000gal water tank foundation design huangyhg 产品功能分析 0 2009-09-07 08:59 AM


所有的时间均为北京时间。 现在的时间是 08:37 AM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多