默认 bonding 920 slabs in high wind zone

bonding (2) slabs in high wind zone
i have a project where there is an anticipated 170 psf suction force on a roof topping slab. the purpose of the slab is to protect the roofing below it. #3 ties were provided in a 6'x5' grid to anchor the slab to the precast double tee roof structure.
a series of unfortunate events for the contractor has resulted in a slab w/o the required reinforcing and the wrong fiber additive.
in lieu of tearing the slab off and starting over, the contractor has come up with the attached detail. they want to drill in new #3 "within an inch or two" of the existing #3. if the two slabs are adequately tied together, the resulting factored suction force is 118 psf or 3540# of hold-down force required per exist #3 tie.
i can't see how there will be adequate force transfer from the new #3 to the existing #3 to prevent the topping slab from becoming airborne during a 300 mph wind event.
opinions anyone? (we can't drill new anchors into the dbl tees as we don't want to perf the vapor barrier that is below the insulation.)
what are you concerned about, is 3540 lbs per #3 existing bars are too high. this is about 31 ksi per bar, which does not seem too high. i am expecting that the very top slab is not yet cast?
depending on the type of bonding agent used, bonding agent itself can transfer 170 psf of uplift without any problem to the slab below. #3 bars on top of the bonding agent is just over kill. try looking into sika armatec-110 epocem.
prescribe, roughened interface and sika armatec and you should be good to go. assuming that you have enough reinforcing to transfer the force to dt.
don't you need 6" to develop a #3 hook? (see aci 12.5)
doesn't look like you can get that here. the hooks would simply pull out of the concrete given enough load.
thanks for the lead. i contacted sika and they suggested sikadur 32 himod in lieu of the armatec 110. do you have experience with that product?
i wasn't concerned about the #3 tensile force being too high. i was concerned about the reality of the force transfer path from the new #3 to the existing #3.
i mostly have experience with armatec as bonding agent. we usually prescribe it because it has a long gel time. which comes in handy if the contractor encounters delay while pouring. any way, while selecting, try to compare the properties of both the agents. why sika recommended 32?
i agree with jae about the hooks. it won't matter what your fix is if you violate another part of the code and nullify your solution.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)
 


主题工具 搜索本主题
搜索本主题:

高级搜索
显示模式

发帖规则
不可以发表新主题
不可以回复主题
不可以上传附件
不可以编辑您的帖子

vB 代码开启
[IMG]代码开启
HTML代码关闭

相似的主题
主题 主题发起者 论坛 回复 最后发表
balcony guardrail wind huangyhg 产品功能分析 0 2009-09-07 02:11 PM
pattern locating tolerance zone shape huangyhg tec-ease(America) 0 2009-09-05 12:06 PM
【转帖】pattern locating tolerance zone shape yang686526 American standards 0 2009-04-29 09:13 PM
【转帖】asme美国机械工程师标准目录2 huangyhg American standards 5 2009-04-26 02:38 PM
mathematical definition of dimensioning and tolerance principles AS<E Y14.5. M - 1994 huangyhg American standards 3 2008-07-03 09:20 AM


所有的时间均为北京时间。 现在的时间是 10:57 PM.


于2004年创办,几何尺寸与公差论坛"致力于产品几何量公差标准GD&T | GPS研究/CAD设计/CAM加工/CMM测量"。免责声明:论坛严禁发布色情反动言论及有关违反国家法律法规内容!情节严重者提供其IP,并配合相关部门进行严厉查处,若內容有涉及侵权,请立即联系我们QQ:44671734。注:此论坛须管理员验证方可发帖。
沪ICP备06057009号-2
更多