查看单个帖子
旧 2009-09-15, 11:59 PM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 snow drift through web of truss above roof

snow drift through web of truss above roof
q1: does anybody know of any snow load provision that takes into account the "openness" of a roof wall type element in regards to snow drift. i've got a new beam on top of an existing roof that acts like a transfer beam for a column to be removed, but it creates snow drifts that overstress the existing roof joists, and new joists are needed in between existing ones. if the beam could be replaced by a truss or joist girder, would that member be open enough through its "web" to allow snow to pass through and not create a drift? the new drift created by the new beam overstresses the existing joists so new joists need to be added in between the existing joists. if the truss did not obstruct the snow and no new drift was created then the existing joist will still work. i've braced the top of the beam with angle kickers at each joist and i would need to do this for the truss as well.
q2: can joist girders have bottom chord bearing?

check out our whitepaper library.
a few questions: 1. what is the ground snow and balanced snow height? 2. what is the depth of your new beam? 3. can a shallower, heavier beam be used so that the beam depth is less than the balanced snow height?
q2....joist girder can definitely be built for bottom chord bearing......just show them what you want.
is your beam less than 15' long? if so, it does not cause drifted snow (per the asce 7 code).
daveatkins
see the attached pdf. it's a new 52' long w36x150 directly above two existing 26' long w18x46 beams with 28' long 20h6 joists on either side. the new beam was designed for the point loads that pick up the existing structure so the existing column can be removed.
it's in fredericksburg, va
here are my snow loads:
ground snow 25 psf
flat roof snow 20 psf
obstruction height 3.5 feet
drift snow 40 psf at high end of triangle
drift length 11'
i like the idea of using a shallower beam. what i'll do is back calculate the maximum drift the existing joists can handle and from that determine a maximum beam depth.
i don't think i attached the file correctly. let me try again.
ok, with the w36 transfer beam and no new joists in between the existing joists, the existing joist were 30% overstressed.
when i found an equivalent w27 size, the existing joists were only 2-3 % overstressed.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)