查看单个帖子
旧 2009-09-10, 11:43 AM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 looking for opinions on the best wa

looking for opinions on the best wa
looking for opinions on the best way to analyze the following situation:
one-way concrete slab reinforced top & bottom both ways, 6 1/2" thick with 1" kalman topping (7 1/2" thick total).
slab supported by wf steel beams @ 6'-8" o.c. with top flange embedded in slab (no shear studs). beams frame into wf steel girders spaced @ 20'-0" o.c. with top flange embedded in slab (no shear studs). beams & girders frame into steel columns on a 20' by 20' grid. slab designed (and confirmed) for 500 psf ll and 100 psf dl.
the problem: the floor is used as a warehouse area, using heavy-duty storage racks typically used on slabs-on-grade. obviously, the storage rack legs create high point loads on the slab. how can i get accurate results for shear, moment, deflection based on this point loading. i need to know if the floor is being overloaded.
it seems to me that applying the loads over a 1' strip of slab and analyzing as a 1' wide conc. beam would be way to conservative. am i right or wrong? any suggestions?
aashto specsfor highway bridges cover point loads on concrete slabs. also see many concrete texts,e.g.,"design of concrete structures, nilson & winter,11th ed.
be sure to check slab for punching shear.
frank hartzell
to space the point loads by hand, i would agree with frank and simply use the aashto equation:
the concentrated load is spread over a distance e
e = (4 + 0.06 x s) but not more than 7 feet (or, i would add, the center to center spacing of the posts).
s = span, ft.\
alternatively, you could use a finite element analysis on the slab, modeling the beams and girders, and get moment contours.
in either case, you should check punching shear through the slab per aci 11.12.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)