查看单个帖子
旧 2009-09-08, 06:30 PM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 development length

development length
folks,
i have a question that may come across as retarded, but i gotta ask.
a standard hook for a #4 bar is 12 db = 12*0.5=6".
what happens for a #4 u bar or a #4 stirrup? is the requirement that you need 2 * standard hook = 24 db to develop the bar?
stirrups are treated differently--there are various ways to develop a stirrup bar. see aci 318-08 section 12.13. and re
no, a 135 degree hook will develop the stirrup, see r12.13.2.2
and don't forget that the 12db is for the straight portion of the hook only - not the bend. the bend is in addition to the straight portion so for a #4 bar the total 90 degree hook size is 8".
see aci 7.1.
folks,
i guess i did not express myself correctly.
a quick sketch:
| |
| |
| |
|____|
?
what is the minimum length (based on db) of the horizontal leg of the u to develop this stirrup?

i think when it is looped around like a "u", you don't have to meet the standard hook distances/lengths....only the bend diameters. so for a #4 stirrup, using 2" for the bend diameter you'd have (out to out of bar):
2" + 2(1/2" bar dia) = 3" total width.
interesting, i am surprised the codes don't address this in any more detail.
another question i have is this:
how much concrete should you have around a reinforcing bar in order to adequately transfer the stresses from reinforcing bar into concrete?
assuming that you have a #5 bar, what is the minimum cylindrical area around the bar needed so that it does not pull out (precluding tension failure in concrete).
your last question depends on development length - you're allowed to not have full contact all the way around as long as you increase the length to compensate
the australian code requires an increase in the development length of around 25% when there is more than 300mm of concrete below a bar (to allow for a void formed under the bar due to the slumping and shrinkage away from the bar of the concrete mass under)
i would assume the minimum cylindrical area is the minimum development length required by your code multiplied by the circumference of your bar
let me rephrase my question:
assuming that you have a #5 bar, what is the minimum cylindrical area of concrete around the bar needed so that it does not pull out.
slickdeals
read chapter 12 of aci. it explains the logic well.
the formula for development is based on the cover/spacing to the bar and the bar diameter. it is not expressed in terms of a cylinder of concrete required.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)