查看单个帖子
旧 2009-09-07, 09:43 AM   #1
huangyhg
超级版主
 
huangyhg的头像
 
注册日期: 04-03
帖子: 18592
精华: 36
现金: 249466 标准币
资产: 1080358888 标准币
huangyhg 向着好的方向发展
默认 aci 318 chapter 20

aci 318 chapter 20
i've got another post going on鈥?
well, i'll post my experience here - but others out there - do add any insights above and beyond this:
i did a load test once on a small grandstand - made of load bearing cmu with double tees forming each riser. no one had a clue where the dt's came from and what load capacity they truly had.
i had a number of barrels set up in a specified spacing to load the grandstand to 125% of the required live loading for grandstands (100 psf i think it was). the loading was performed by adding water to the barrels - calculating the volume in each barrel, the resulting weight, and the barrel spacing to mimic 100 psf.
i took vertical elevation measurements of the dt's prior to loading, at 1/4 loading, 1/2, 3/4 and full loading. then removed the load, took measurements, and then took them again i think at 24 hours later. (i don't have aci with me right now but this is what i recall).
aci provided design criteria for the deflection and deflection-rebound.
__________________
借用达朗贝尔的名言:前进吧,你会得到信心!
[url="http://www.dimcax.com"]几何尺寸与公差标准[/url]
huangyhg离线中   回复时引用此帖
GDT自动化论坛(仅游客可见)