orsion on a loose lintel supporting brick
torsion on a loose lintel supporting brick
i am trying to check the torsion of a loose lintel vs the bia-recommended limit of 1/16"....but i can't find the "j" of steel angle shapes for my t*rho/j formula. does anyone know where i can find j of angles? can i just take j=ixx+iyy? thanks i can't re the aisc manual has a table of torsional properties for hot-rolled shapes. see part 1 of the third edition lrfd, part 1 of the ninth edition asd, or aisc design guide 9. if you are outside of the us, you'll have to check your own references and manuals, but it shouldn't be a mystery. note that ix+iy is the polar moment of inertia, not the torsion constant. i didn't see j in part 1 of 2nd ed'n or 3rd ed'n of lrfd or j in asd...j's not in there. begin on page 1-117 of the 9th edition asd or 1-89 or the 3rd edition lrfd. ah! gotcha...thank you for open sections (such as angles), the torsional constant j is equal to (1/3)*the sum of b*t^3 of all the pieces. |
所有的时间均为北京时间。 现在的时间是 05:05 PM. |