if i have anchor bolts embedded in a cmu wall (f'm=1500psi)that is fully grouted (grout f'c=4000psi), is it ok to use the shear strength values from 1997 ubc table 19-d for bolts embedded in concrete, rather than the values listed in table 21-e for bolts embedded in masonry? or do the values for masonry already take into account fully grouted units with higher strength grout? i think your problems can be best answered by a question also. who鈥檚 holding the grout? i will use the values listed in bolts embedded in masonry, even if it is 1,000,000psi grout (just exaggerating). for your second question, my answer is 鈥?perhaps they already consider a certain strength of grout but maybe not higher 鈥? many thanks. |
所有的时间均为北京时间。 现在的时间是 04:27 AM. |