opening in one-way slab
opening in one-way slab
i've been asked by a contractor if it's ok to cut a opening in a one-way spanning slab. details are on the attachemnt and are as follows: - 125mm thick, rebar not known - spanning 3300mm from wall onto steel beam - opening is 310x260mm at corner i'm aware of rules governing the positioning and size of openings for 2 way spanning slabs however there seem to be very little on 1 way spanning slabs. my thoughts are rebar will be hit and the slab will lose some of its strength however due to the size and the location adjacent to 2 walls the slab will be ok with needing secondary steelwork or strengthening. any thoughts? it is only 260 (10.5") in the direction that the slab is spanning, run a covermeter over it, the opening hopefully only cuts 1 bar maximum, it is in a low moment region so hopefully the slab with still have enough capacity in that region. is the wall running left to right along the page loadbearing? i would not hesitate to cut the hole in this location. a crack could propagate from the corner, but it would be of no consequence. i would prefer a circular hole for easy of coring, even so i wouldn't hesitate, just make sure they don't over cut too much. when in doubt, just take the next small step. |