minimum conc. column size
minimum conc. column size
are there any aci provisions for minimum (tied) column width? i'm trying to match 8 inch cmu with an 8x16 column and i know it not the easiest to construct with 1.5 inch clearance. would there be an opportunity to reduce the cover to 3/4 inch, similar to a conc. wall. i wonder what the tilt-up association uses for tied wall piers/columns. tia find a job or post a job opening check the section on slenderness effects in compression be careful with your fire ratings on a column that small as well. i've gone down to 10" columns in stairwells - but not smaller - you'd have trouble getting your ties to fit and your vertical bars get so bunched together that you might have trouble getting concrete consolidated below. we have 8-inch wide columns on many projects. they're a pain but possible. |