几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量

几何尺寸与公差论坛------致力于产品几何量公差标准GD&T (GDT:ASME)|New GPS(ISO)研究/CAD设计/CAM加工/CMM测量 (http://www.dimcax.com/hust/index.php)
-   产品功能分析 (http://www.dimcax.com/hust/forumdisplay.php?f=10)
-   -   metal panels for bottom chord truss bracing (http://www.dimcax.com/hust/showthread.php?t=26414)

huangyhg 2009-09-10 01:41 PM

metal panels for bottom chord truss bracing
 
metal panels for bottom chord truss bracing
i am trying to verify if 29 ga. mcelory maxi-rib panels are sufficient for the permanent bc lateral bracing of a wood truss roof (are the panels a rigid clg. diaphragm?). the trusses are scissor trusses spaced at 4' o.c. and spanning 60 ft. the building is 80' long. i question if the panels are good enough on their own, or, if we should add clb's.
find a job or post a job opening
suggest you add braces at the intervals required.
ba
i spoke with an engineer from mcelroy regarding this question. he confirmed that the 4' spacing is probably too much for this panel. he recommended at 24 ga. panel, or, choosing the mega-rib panel (1 1/2" ribs) at 29 ga. or, of course we could use the maxi-rib if we added clb's at 24" o.c.
thanks for your response


所有的时间均为北京时间。 现在的时间是 06:08 AM.